    Stage 2 heat is cooling, what am I missing?

    Hey, I recently got installed my thermostat (honeywell th8320U), by the second service company i ve called to do work on my heating system.

    The first company I've called told me I have a 1 heat / 1 cool system. After the technician left, my heating and cooling system were no longer working. Called him and said it isn't working, and he said he will be coming back to check on it, retried calling him and the phone number is no longer active. Called a second technician, and now this tech is saying i ve got a very good system at 3 stage heat/ 2 stage cool. He specified that my heat pump is 2h/2c and inside my emergency heat. I originally thought, since the other tech told me 1h/1c, that the unit outside was only for the cooling and the unit inside the electric furnace. Turns out its a complete heat pump. Good news of course, more efficient. So now I get the tech to install my termastat, and says he is not familiar with the heat pump system... great. Now my stage 1 heat heats properly, but when my stage 2 heat kicks on it starts to cool...

    Woke up this morning and it was 16 degrees in the house instead of 21. Cold air coming out of the ducks.

    Here is how he wired it,

    Thermastat heatpump Furnace
    RC/R (jumper)---------RC-----------------RC
    W and O/B together---W and O/B--------N/A
    Y---------------------Y----------------N/A
    G---------------------------------------G (Fan)
    C---------------------C-----------------C
    Aux-------------------W1/66-----------N/A
    E---------------------------------------E (stage 3 electric heat (used under -10c))
    Y2 not wired to anywhere
    L not wired to anywhere

    This is a single transformer setup on 24v.

    What the heck did he do wrong?

    Kinda skeptical calling another tech at the moment, they all seem to mess it up.

    Any advice from the pros here?

    Would be great help, as I've spent ovet 1200$ so far and my system still isnt working.

    Thanks

    A. LeBlanc

  2. #2
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    68,981
    A whole $1,200 for a new heating system, eh? Sounds to this pro like you never had much a real pro working equipment you bought via the internet. If I'm wrong, I apologize. Either way, you need to have a real professional sort out your problems.

    If you believe that all professionals seem to "mess it up", why in the world would you be looking for help here?
    Government is a disease...
    ...masquerading as its own cure…
    Ecclesiastes 10:2 NIV


  3. #3
    Join Date
    Dec 2002
    Location
    Houston,Tx.
    Posts
    16,122
    Quote Originally Posted by RoBoTeq View Post
    A whole $1,200 for a new heating system, eh? Sounds to this pro like you never had much a real pro working equipment you bought via the internet. If I'm wrong, I apologize. Either way, you need to have a real professional sort out your problems.

    If you believe that all professionals seem to "mess it up", why in the world would you be looking for help here?
    Hey! do you have your glasses on? you made a wrong turn back there at the ARP/RES sign.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards". - Vernon Law

    "Never let success go to your head, and never let failure go to your heart". - Unknown

  4. #4
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    68,981
    Quote Originally Posted by Mr Bill View Post
    Hey! do you have your glasses on? you made a wrong turn back there at the ARP/RES sign.
    I'm a very diverse and complex person, Bill.
    Government is a disease...
    ...masquerading as its own cure…
    Ecclesiastes 10:2 NIV


  5. #5
    Join Date
    Dec 2002
    Location
    Houston,Tx.
    Posts
    16,122
    Quote Originally Posted by RoBoTeq View Post
    I'm a very diverse and complex person, Bill.
    Yes I can see that.....
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards". - Vernon Law

    "Never let success go to your head, and never let failure go to your heart". - Unknown

  6. #6
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    7,772
    Lots of techs don't understand how York/Coleman heat pumps are wired to work correctly, call a company that deals in York equipment and they should be able to set it up properly.

  7. #7
    Join Date
    Oct 2012
    Posts
    8
    Hi,

    I haven't purchased a new system, only using the one that was already in the house. Sorry if I have lead you to believe that it is a new system.

    Alright I ll check with other companies.

    Although I am curious to know what w1/66 is on the heat pump. Any ideas?

    Thanks

    A. LeBlanc

  8. #8
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    7,772
    W1/66 is what energizes electric heat during the defrost cycle

  9. #9
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    7,772
    Y2 needs to be wires from tstat and probably to indoor to change blower speed. What is model # of indoor and outdoor units

  10. #10
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    68,981
    This is becoming a DIY instructional thread.
    Government is a disease...
    ...masquerading as its own cure…
    Ecclesiastes 10:2 NIV


  11. #11
    Join Date
    Oct 2004
    Location
    So Cal
    Posts
    3,612
    They don't need to be a HP York or Coleman specialist. They need to know how to read a friggin wiring diagram.
    Sad.

  12. #12
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    68,981
    Quote Originally Posted by precision hvac View Post
    They don't need to be a HP York or Coleman specialist. They need to know how to read a friggin wiring diagram.
    Sad.
    Assuming that "they" are HVAC professionals.
    Government is a disease...
    ...masquerading as its own cure…
    Ecclesiastes 10:2 NIV


  13. #13
    Join Date
    Feb 2007
    Location
    Fremont, Indiana
    Posts
    1,750
    Quote Originally Posted by RoBoTeq View Post
    This is becoming a DIY instructional thread.
    Amen

    sent from my Samsung Galaxy Note
    Member of the "Work Exchange Program"
    "Will work for knowledge"

    "Everyone is a genius. But if you judge a fish on its ability to climb a tree, it will live its whole life believing that it is stupid"
    A Einstein

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event