Thread: Goodman HP with Propane or Electric Aux heat?

  1. #21
    Join Date
    Jul 2008
    Location
    Rochester NY
    Posts
    5,298
    Post Likes
    Quote Originally Posted by pendetim View Post
    Thanks for all the insight, folks.

    I will be having a re-quote done on a 2 stage 10KW electric backup, removing the propane furnace. I suspect the capital cost will be pretty close as I will need to run a 60A service about 80' from the garage to the crawl space for the strips.

    As pointed out, this will make the heat staging a little more complex as I will want to be able to stage Y, Y2, W and W2. Would the EcoBee EB-STAT-02 be a good candidate for this?
    I believe it would. I'm having great fun with mine. Putting 2 more in this weekend.

    That said, the ability to truly communicate with the equipment is like the difference between a 1999 motorola flip phone and a droid razr maxx.

    So if you get communicating equipment (ie Carrier or American Standard), get the manufacturers communicating thermostat.

  2. #22
    Join Date
    Aug 2001
    Location
    Pavilion, NY
    Posts
    4,437
    Post Likes
    Assuming equal cost,,, I would rather have a toaster oven with resistance heaters that last forever and a relatively simple control board in a unit that requires essentially no maintenance over a unit that has multiple pressure switches, gas valves, condensate drains, inducer motor, and igniters to fail and requires far more service. If you factor a 20yr lifespan my money says you will have far less invested in your system with electric backup.
    ...

  3. #23
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    Quote Originally Posted by kangaroogod View Post
    Assuming equal cost,,, I would rather have a toaster oven with resistance heaters that last forever and a relatively simple control board in a unit that requires essentially no maintenance over a unit that has multiple pressure switches, gas valves, condensate drains, inducer motor, and igniters to fail and requires far more service. If you factor a 20yr lifespan my money says you will have far less invested in your system with electric backup.
    Is there anywhere in the U.S. where you can get a Btu of heat from an electric heater for the same cost in energy as a Btu of heat from a gas furnace would cost?

    Ass-u-me?
    Training is important!
    Practical Training is a must!

  4. #24
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,331
    Post Likes
    Quote Originally Posted by RoBoTeq View Post
    Is there anywhere in the U.S. where you can get a Btu of heat from an electric heater for the same cost in energy as a Btu of heat from a gas furnace would cost?

    Ass-u-me?
    ((((((((( I would guess Kansas City might be close with extremely low electric rate.
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  5. #25
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    Quote Originally Posted by RoBoTeq View Post
    Is there anywhere in the U.S. where you can get a Btu of heat from an electric heater for the same cost in energy as a Btu of heat from a gas furnace would cost?

    Ass-u-me?
    He was using propane as backup. Electric resistance and propane are comparable in our area. Natural gas is of course the clear winner for fuel cost, but also remember to factor in the meter fees.

  6. #26
    Join Date
    Aug 2001
    Location
    Pavilion, NY
    Posts
    4,437
    Post Likes
    Given his choices of propane or electric and using the rates provided it would be $3.13 a therm for propane and $3.22 a therm for electric. Based in the fact that the balance point is 30 degrees he will be using essentially all propane below 30 but with the heat pump he will be able to run the unit down to the design temp of 15 degrees with a cop of 2.75 (21200 but output) and supplement the balance of 12800 btus at essentially the same cost of propane. The big difference is that he will only need to heat 12800 btus at $3.22 and the 21200 btus at a bonus of $1.17 a therm instead of 34000
    Btus at $3.13........If my math is correct......$1.09 per hour on propane and $.67 an hour on heatpump with electric backup. No brainier for me. Ass-u-me??? The verdict is still out
    Last edited by kangaroogod; 10-17-2012 at 09:38 PM.
    ...

  7. #27
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    To stage 10kw, someone would have to redo the controls on the heat kit. Usually it would take 15kw and up to stage.

    Jim, Rheem hasn't replaced demand with time in ages. That was the way they replaced the Ranco DD1 board in the early 90s. Now it is 100% demand and replaced that way. I don't think ICP has been demand in some time either. They used the DDL board Rheem used for a short time. That board was unreliable. They went back to timer, Rheem found a different vendor with a more reliable board. I assume York has a lot of demand boards still. Lennox/Allied in select high end units. Actually Allied in the 16 SEER but not the 18 SEER. I think they needed it to get a HSPF target. Obviously Trane has been demand forever. Oh, and Nordyne on high end too. Still want to replace my time board with the board out of the FT4BF. Looks like it will work!

  8. #28
    Join Date
    Jul 2008
    Location
    Rochester NY
    Posts
    5,298
    Post Likes
    Quote Originally Posted by kangaroogod View Post
    Given his choices of propane or electric and using the rates provided

    balance point is 30 degrees

    all propane below 30

    with the heat pump he will be able to run the unit down to the design temp of 15 degrees with a cop of 2.75 (21200 but output) and supplement the balance of 12800 btus at essentially the same cost of propane.

    The big difference is that he will only need to heat 12800 btus at $3.22 and the 21200 btus at a bonus of $1.17 a therm instead of 34000 Btus at $3.13........If my math is correct......

    $1.09 per hour on propane and $.67 an hour on heatpump with electric backup. No brainier for me. Ass-u-me??? The verdict is still out
    That's what I was thinking! Propane and straight electric basically =. Depending upon common temperatures, that propane might run a lot, and the resistance not much at all.

    And if it's like my mom's 2 stage Infinity, the pump just might just heat the house down to 7f NEVER requiring the backup.

    *She's on NG. The reason we know it heats the house to 7f, they accidentally locked the furnace out at install. She called me on a 7f night wondering if there was a problem because the register air "felt a little cool". She wasn't terribly concerned "because the house was still 70", but thought she better check with me JIC.

  9. #29
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by BaldLoonie View Post
    To stage 10kw, someone would have to redo the controls on the heat kit. Usually it would take 15kw and up to stage.

    Jim, Rheem hasn't replaced demand with time in ages. That was the way they replaced the Ranco DD1 board in the early 90s. Now it is 100% demand and replaced that way. I don't think ICP has been demand in some time either. They used the DDL board Rheem used for a short time. That board was unreliable. They went back to timer, Rheem found a different vendor with a more reliable board. I assume York has a lot of demand boards still. Lennox/Allied in select high end units. Actually Allied in the 16 SEER but not the 18 SEER. I think they needed it to get a HSPF target. Obviously Trane has been demand forever. Oh, and Nordyne on high end too. Still want to replace my time board with the board out of the FT4BF. Looks like it will work!
    The local supply house must have had an old T&T in stock then. I did one last winter, and they gave me a T&T instead of on demand.

    Haven't installed a new ICP for a few years now, didn't realize they changed.

    Lower end yorks are still T&T.

Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •