10-14-2012, 05:22 AM #11On demand defrost uses the temp difference between the air and the liquid line to determine if there is ice/frost on the coil to a point that it needs to be defrosted. After the outdoor temp drops below X degrees(varies with manufacturer) they won't go into defrost except for once every 6 hours of compressor run time to make sure the outdoor coil doesn't become oil logged.I was led to believe these things understood defrost based upon temperature. Given the source of the contradiction, I had to dig. I guess pressure increase does not trigger defrost. What does is really not very clear to me but probably will be to you:
Ideal Defrost / Intelligent Defrost - (I have the Carrier VNA service training manual)
What is not clear is it somehow knows how long defrost takes, and based upon that sets the next defrost run interval.
This thing is pretty amazing. The controller can manage refrigerant charging check, pump down, tells suction pressure, compressor rpm, suction temp, superheat, exv position, airflow, lbs of refrigerant to add or subtract based on lineset length...
And in a mild climate where the btu cost of propane has a snowballs chance in hell of approaching the cost of high cop heat pump, having a few btu of electric resistance combined with the heat pump for a few hours a winter is going to be WAY WAY cheaper than paying the incremental on the furnace. Paying the additional cost of burning propane particularly when you factor the heat pump CAN run with the resistance (like an additional stage) and the propane CAN NOT.
I simply have not heard of 50c kwh electric, if it exists it's very rare, and that's still cheaper than propane at most temps.
Forward energy view is electric will become more and more closely tied to natural gas. The only source that can hold a candle to the btu cost of these high COP heat pumps is Natural Gas, and that requires some pretty cold temperatures. This is very likely to remain true for a long time.
Carrier tries to mimic the efficiencies of on demand defrost. But misses the boat a bit. Its better then just time and temp defrost, but still activated by only coil temp and compressor run time(with respect to outdoor temp being under 50). But when its 10 degrees outside, Carriers Ideal will still do needless defrost cycles. On Demand won't.
Quick Navigation
AOP Residential HVAC
Top
- Site Areas
- Settings
- Private Messages
- Subscriptions
- Who's Online
- Search Forums
- Forums Home
- Forums
- Welcome & Introduction
- General Forum
- Ask Our Pro's-Owner Assistance
- The ARPA Zone/Open Technical Discussion Forums
- General Discussion
- Tech to Tech Chat - Residential
- Tech to Tech Chat - Commercial
- Refrigeration & Ice Making
- Controls
- Chillers Open Forum
- Commercial Food Service Equipment
- Going Green: Geo Thermal / Water Source
- Indoor Air Quality
- Fireplaces
- Tools & Test Equipment
- Food and Grill Forum
- "Wall of Pride" - Pictures
- "Wall of Shame" - Pictures
- Electrical General Forum
- Welcome from the Editor & Electrical Forum Rules
- What's new on EC&M Magazine
- Open Discussion Electrical
- Lighting & Lighting Controls
- Renewable Energy
- New Products
- Bonding & Grounding
- Motors & Motor Controls
- Test & Measurement
- Tools & Equipment
- Pro's Forum: National Electrical Code (NEC)
- Pro's Forum: Electrical Safety
- Pro's Forum: Power Quality
- Pro's Forum: Calculations & Electrical Theory
- Pro's Forum: Electrical Business & Marketing
- Pro's Forum: Estimating
- Job Postings
- Carnak Zone/Locked Areas - For Professional Member Only
- Pro Membership Information
- Pro's Forum: Business & Marketing
- Pro's Forum: Sales
- Pro's Forum: Residential
- Pro's Forum: Commercial
- Pro's Forum: Geo Thermal / Water Source
- Pro's Forum: Refrigeration & Ice
- Pro's Forum: Chillers
- Pro's Forum: Oil Burners
- Pro's Forum: Hydronics/Boilers
- Pro's Forum: Building Science Discussions
- Pro's Forum: Training and Education
- Pro's Forum: Tips 'n Tricks of the Trade
- Comanche Marketing
- Educational Forums - Professional Members Only
- Welcome to HVAC-Talk's Educational Forums
- Basic Principles & Theory
- HVACR Equipment, Components & Accessories
- Residential HVAC
- Commercial HVAC
- Commercial Refrigeration & Supermarkets
- Refrigerants
- Refrigerant Oils
- Fuels
- Duct Systems Design, Installation & Practice
- Piping Systems Design, Installation & Practice
- Control System Design, Installation & Practice
- HVACR Software, Calculators & Apps
- HVACR Service & Troubleshooting
- The Educational Forums Challenge Quizzes
- Glossary of HVACR Terminology
- Miscellaneous Forums
«
Previous Thread
|
Next Thread
»



Reply With Quote