Thread: York 5 ton heat exchangers
Hybrid View
-
10-12-2012, 08:25 PM #1
Regular Guest
- Join Date
- Jun 2012
- Posts
- 6
York 5 ton heat exchangers
Finding lots of cracked York exchanges this year as usual. I have found one screw on the bottom section of the heat exchanger behind the burner controls section a huge pan in the a** to remove. Am I alone in this trouble and are there any tricks for getting this I am not aware of? I find I usually just take out the blower and reach around with a open end wrench which works until the screw strips
-
10-13-2012, 05:07 PM #2
I use a pocket cresent wrench. It's still a PITA.
-
10-13-2012, 10:59 PM #3
Professional Member*
- Join Date
- Dec 2010
- Location
- The Quad-Cities area (midwest).
- Posts
- 1,760
Are these cracked H. E. on the 80% or 90% furnaces? You meant to say furnaces with the 5 ton blowers?
Do you remember the size of the filters used or which side of the furnace the RA drop is on?
Does York have a reason for this happening or do they say it's because of a poor installation?
-
10-13-2012, 11:49 PM #4
Professional Member
- Join Date
- Sep 2007
- Location
- NH
- Posts
- 918
-
10-14-2012, 06:08 AM #5
Professional Member*
- Join Date
- Dec 2010
- Location
- The Quad-Cities area (midwest).
- Posts
- 1,760
-
10-13-2012, 11:47 PM #6
Professional Member
- Join Date
- Sep 2007
- Location
- NH
- Posts
- 918
-
10-14-2012, 12:36 AM #7
Regular Guest
- Join Date
- Jun 2012
- Posts
- 6
I am talking 5 ton package RTU. Filters are 2 15x20x2 and 1 14x25x2. Installation is fine, I believe it is just a problem with these particular York units that the heat exchangers have a tendency to crack. I have also tried the multiple extension bits with 5/16 bit on the end to remove that effen screw however I need to remove the screws for the burner control section and hammer the panel back just to get a bit on the screw.... what a pain
-
10-14-2012, 07:48 AM #8
Depending on the unit, I use either a 1/4 x 5/16 offset box ratchet, or an extension.
I bend the tube supports inward for removal of the old HX, and I slide sheet metal down the sides over the insulation (hanging on the top edge of the sides) to place the new HX into place without ripping up the insulation.[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
-
10-17-2012, 09:37 PM #9
Professional Member
- Join Date
- Sep 2007
- Location
- NH
- Posts
- 918
-
10-14-2012, 08:17 AM #10
Any of you ever tried putting a piece of sheetmetal on sides of HX while removing and installing? One of the techs in my company did this to protect insulation and I believe it worked.
-
10-16-2012, 09:53 PM #11[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
-
10-14-2012, 08:49 AM #12
York sunline heat exchangers are i.m.o by far the most time consuming ones to replace. I'm glad they decided to sandwich the insulation between metal at the factory now. It's just the screws and taking apart everything ...
Sent from my HTC Sensation 4G using Tapatalk 2
-
10-16-2012, 10:12 PM #13
If the furnaces were tuned with CA, airflow was set correctly, and a 2 min post purge was installed, then we wouldn't have to replace these heat exchangers so often.
but, then a lot of us would be short on a job.