    Have a customer with a 25 ton water cooled chiller that wants the high and low pressure switches tested on his refrigeration equipment. The switches are the encapsulated type. I need to confirm the switches work, not just remove wires from the switch. Customer does'nt want me running the discharge pressure up and having the suction pressure drop artificially to trip the switches. Has anyone removed all the refrigerant or added tubing or small valves to isolate the switches to make this test with nitrogen?
    I need to do the test every year.
    ENJOY THE RIDE

  2. #2
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Post Likes
    Most encapsulated pressure switches are mounted on schroeder cores, not all call manufacturer to find out for sure. If they are just pop them off and test with nitro on a manifold. If they are not you may have to pull it down. I'd put them back on Schroeders so next year you don't have to pull it down.

  3. #3
    Join Date
    Mar 2004
    Location
    SE Michigan
    Posts
    22,178
    Post Likes
    Whats a shroeder core? Unless you mean shrader valve core?
    “Socialism is a philosophy of failure, the creed of ignorance, and the gospel of envy, its inherent virtue is the equal sharing of misery.”

  4. #4
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Post Likes
    Quote Originally Posted by coolwhip View Post
    Whats a shroeder core? Unless you mean shrader valve core?
    . iPhone.

  5. #5
    Join Date
    Mar 2004
    Location
    SE Michigan
    Posts
    22,178
    Post Likes
    lolz!
    “Socialism is a philosophy of failure, the creed of ignorance, and the gospel of envy, its inherent virtue is the equal sharing of misery.”

  6. #6
    Join Date
    Dec 2010
    Location
    On a Peninsula in NE NC
    Posts
    1,904
    Post Likes
    Do not put a high pressure safety device on a valve, and low only on a king valve, not ball style.

    Would rather them be on schrader's though.

    Second calling mfg for info

  7. #7
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Post Likes
    Quote Originally Posted by Southern Mech View Post
    Do not put a high pressure safety device on a valve, and low only on a king valve, not ball style.

    Would rather them be on schrader's though.

    Second calling mfg for info
    Absolutely rite! Schraders only. Never ever put a high pressure safety on a valve that can be closed. Bad things can happen.