Page 2 of 3 FirstFirst 123 LastLast
Results 14 to 26 of 27
  1. #14
    Join Date
    Oct 2012
    Location
    Israel
    Posts
    4
    Post Likes

    Sorry, I didn't notice

    Quote Originally Posted by berg2666 View Post
    There is more then four stages here, each condensor has two stages.
    Anyway, you can use an aditional 4 stage simple thermostat. Don't worry about the head pressure control
    of the comps. it's probably in the condense units.
    I forgot to mention that you must install a seperate water pump with a check valve on the discharge side
    for each heat exchanger and please don't forget the safety devices such as water flow switch and freeze protector
    for each heat exchanger. Cheers

  2. #15
    Join Date
    Nov 2005
    Location
    Shreveport, Louisiana
    Posts
    2,338
    Post Likes
    Quote Originally Posted by Letonil View Post
    Anyway, you can use an aditional 4 stage simple thermostat. Don't worry about the head pressure control
    of the comps. it's probably in the condense units.
    I forgot to mention that you must install a seperate water pump with a check valve on the discharge side
    for each heat exchanger and please don't forget the safety devices such as water flow switch and freeze protector
    for each heat exchanger. Cheers
    And your thoughts on the bypass valve???
    UA Local 141

  3. #16
    Join Date
    Sep 2010
    Posts
    8
    Post Likes
    Thread Starter
    I am using a DDC based control system because it gives me the best control of the system, and the fancoil units in the house. I already have done all things for protecting the system including: freezestat, dp switch (is more accurate than a flow switch), on/off control valves for HX when full load is not neccesarry, planning on putting high and low ref pressure sensors to communicate to the controler. These CU start using the big compressor and when the load is acheived the small compressor starts that is the way the units saves energy. The thing with the CU is that if you do it wrong the compressors start failing and after a couple of failures Tranes does not warranty them at least locally this is my main problem. Have known of this problem from an early experience from another contractor but the system was with a multiple cu units split system.

  4. #17
    Join Date
    Oct 2012
    Location
    Israel
    Posts
    4
    Post Likes

    what bypass?

    Quote Originally Posted by berg2666 View Post
    And your thoughts on the bypass valve???
    What bypass valve?

  5. #18
    Join Date
    Apr 2012
    Location
    Louisiana
    Posts
    916
    Post Likes
    Looks like fun, sounds like you've got it covered. Ive done a few retrofits but never just built my own chiller.
    Let us know how it turns out.

  6. #19
    Join Date
    Sep 2010
    Posts
    8
    Post Likes
    Thread Starter
    Quote Originally Posted by Letonil View Post
    What bypass valve?
    Due to the system been built with two way control valves the system needs a bypass with a proportional control valve to relieve system pressure when valves start to close.

  7. #20
    Join Date
    Nov 2005
    Location
    Shreveport, Louisiana
    Posts
    2,338
    Post Likes
    Quote Originally Posted by Letonil View Post
    What bypass valve?

    Please read the whole post and you will find mention of a bypass valve.


    You will find out that if you come to this forum and only read the first post and then comment without reading all that your opinion will eventually become null and void because people will learn that you are not paying 100 percent attention to what you are reading.
    UA Local 141

  8. #21
    Join Date
    Nov 2005
    Location
    Shreveport, Louisiana
    Posts
    2,338
    Post Likes
    Did you decide who's DDC controls you will use????
    UA Local 141

  9. #22
    Join Date
    Sep 2010
    Posts
    8
    Post Likes
    Thread Starter
    Will present Pros/cons to the owner and let them decide! Still waiting for the answer to my first question that was if it was you which controls company would you use? I am still waiting for some parts to arrive like pumps some control valves, chilled water insulation will be done too, etc

    Air handling side work is already done except grills and diffusers.

  10. #23
    Join Date
    Nov 2005
    Location
    Shreveport, Louisiana
    Posts
    2,338
    Post Likes
    Quote Originally Posted by jborges View Post
    Will present Pros/cons to the owner and let them decide! Still waiting for the answer to my first question that was if it was you which controls company would you use? I am still waiting for some parts to arrive like pumps some control valves, chilled water insulation will be done too, etc

    Air handling side work is already done except grills and diffusers.

    Cannot answer that question correctly as I do not know anything about Trends products but you are the one with the final answer and sounds like some knowledge of Trends product
    UA Local 141

  11. #24
    Join Date
    Apr 2009
    Location
    HR
    Posts
    49
    Post Likes
    Quote Originally Posted by jborges View Post
    Hi my name is Javier Borges I am from PR right now I am installing 20 Tons Chilled water system using 4 Trane 4TTZ060 condensing units and 2 10 tons plate HX. Right now I have trouble deciding which DDC Controls to use should I use Trane Controls (++++++++++ Expensive) or my trusted control supplier which supplies Trend Controls. For those of you that do not know these trane units have two compressors inside of them and requiere a special wiring harness to connect them to any control either Trane or Trend. Please reccommend thanks.
    Hi,
    I'm not familiar with those two, but did you checked the Siemens Climatix series OEM controllers? They offer two basic variants, one for chiller control an done for heating substations. The controllers are freely programmable, can communicate over a range of buses (KNX, LON, Modbus, Mbus, BACnet) and they are cheap. The learning curve is pretty steep, but the starter curse helps you much, I can help you here also.

  12. #25
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    6,078
    Post Likes
    Quote Originally Posted by zlotvor View Post
    ...but the starter curse helps you much...
    i have worked on starters that have been cursed before.
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

  13. #26
    Join Date
    May 2002
    Posts
    948
    Post Likes
    I see 8 stages here ,not four ....
    mikeacman

Page 2 of 3 FirstFirst 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.