Sorry, I didn't notice
Anyway, you can use an aditional 4 stage simple thermostat. Don't worry about the head pressure control
of the comps. it's probably in the condense units.
I forgot to mention that you must install a seperate water pump with a check valve on the discharge side
for each heat exchanger and please don't forget the safety devices such as water flow switch and freeze protector
for each heat exchanger. Cheers
-
10-16-2012, 03:11 PM #15
Professional Member
- Join Date
- Nov 2005
- Location
- Shreveport, Louisiana
- Posts
- 2,255
-
10-17-2012, 09:09 AM #16
Regular Guest
- Join Date
- Sep 2010
- Posts
- 8
I am using a DDC based control system because it gives me the best control of the system, and the fancoil units in the house. I already have done all things for protecting the system including: freezestat, dp switch (is more accurate than a flow switch), on/off control valves for HX when full load is not neccesarry, planning on putting high and low ref pressure sensors to communicate to the controler. These CU start using the big compressor and when the load is acheived the small compressor starts that is the way the units saves energy. The thing with the CU is that if you do it wrong the compressors start failing and after a couple of failures Tranes does not warranty them at least locally this is my main problem. Have known of this problem from an early experience from another contractor but the system was with a multiple cu units split system.
-
10-17-2012, 02:14 PM #17
New Guest
- Join Date
- Oct 2012
- Location
- Israel
- Posts
- 4
-
10-17-2012, 04:15 PM #18
Looks like fun, sounds like you've got it covered. Ive done a few retrofits but never just built my own chiller.
Let us know how it turns out.
-
10-18-2012, 08:02 AM #19
Regular Guest
- Join Date
- Sep 2010
- Posts
- 8
-
10-18-2012, 06:48 PM #20
Professional Member
- Join Date
- Nov 2005
- Location
- Shreveport, Louisiana
- Posts
- 2,255
Please read the whole post and you will find mention of a bypass valve.
You will find out that if you come to this forum and only read the first post and then comment without reading all that your opinion will eventually become null and void because people will learn that you are not paying 100 percent attention to what you are reading.UA Local 141
-
10-18-2012, 06:50 PM #21
Professional Member
- Join Date
- Nov 2005
- Location
- Shreveport, Louisiana
- Posts
- 2,255
Did you decide who's DDC controls you will use????
UA Local 141
-
10-18-2012, 07:33 PM #22
Regular Guest
- Join Date
- Sep 2010
- Posts
- 8
Will present Pros/cons to the owner and let them decide! Still waiting for the answer to my first question that was if it was you which controls company would you use? I am still waiting for some parts to arrive like pumps some control valves, chilled water insulation will be done too, etc
Air handling side work is already done except grills and diffusers.
-
10-19-2012, 09:09 PM #23
Professional Member
- Join Date
- Nov 2005
- Location
- Shreveport, Louisiana
- Posts
- 2,255
-
10-25-2012, 05:26 PM #24
Professional Member
- Join Date
- Apr 2009
- Location
- HR
- Posts
- 27
Hi,
I'm not familiar with those two, but did you checked the Siemens Climatix series OEM controllers? They offer two basic variants, one for chiller control an done for heating substations. The controllers are freely programmable, can communicate over a range of buses (KNX, LON, Modbus, Mbus, BACnet) and they are cheap. The learning curve is pretty steep, but the starter curse helps you much, I can help you here also.
-
10-25-2012, 06:17 PM #25
-
10-26-2012, 07:29 AM #26
Professional Member
- Join Date
- May 2002
- Location
- evansville indiana
- Posts
- 892
I see 8 stages here ,not four ....