Home Made Chiller with Trane 4TTZ060 Condensing Units
Hi my name is Javier Borges I am from PR right now I am installing 20 Tons Chilled water system using 4 Trane 4TTZ060 condensing units and 2 10 tons plate HX. Right now I have trouble deciding which DDC Controls to use should I use Trane Controls (++++++++++ Expensive) or my trusted control supplier which supplies Trend Controls. For those of you that do not know these trane units have two compressors inside of them and requiere a special wiring harness to connect them to any control either Trane or Trend. Please reccommend thanks.
20121011_104127.jpg
-
10-12-2012, 04:42 PM #2
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,550
Are these the kind of units that have a small compressor and a large compressor?
-
10-12-2012, 05:28 PM #3
Sounds like fun although I'm not familiar with either control systems you mention. Are these units 2 stages? Seems to me like you need something that will the number of stages in addition to a leaving water sensor, freezestat, and all that. How are you going to control the pump? What kind of application is this going to be used it?
-
10-12-2012, 09:57 PM #4
is it just me or do the txv external equalizer lines look like they are going to the wrong suction line?
Time to get my nerd on!
-
10-12-2012, 10:58 PM #5
-
10-12-2012, 11:20 PM #6
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,550
-
10-12-2012, 11:32 PM #7
Professional Member
- Join Date
- Mar 2011
- Location
- North Carolina Piedmont Area
- Posts
- 309
Looks like a clean job.
Who makes that pipe isolator for the uni-strut clamp?
Have you thought of adding a liquid line solenoid valve to prevent migration. Does that condenser have a suction accumulation to prevent liquid slugging on start up or is it even necessary?
As far as Trend goes they make a good control as long as you have the support.
-
10-13-2012, 07:15 AM #8
Regular Guest
- Join Date
- Sep 2010
- Posts
- 8
The units are the one that have the double compressor and they are going to be used on high end residence for chilled water. I have already consider a freezestat, and every other sensor in that need to be done. The pumps will be controlled with the same DDC controls that will be installed with DPS and Transmitter for bypass valve. This is my third system that I have built but never with these condensing units. The hx suction and liquid connections are crossed blow them with nitrogen before doing installation.
Those isolators are electrical PVC Pipe cut at 3"
-
10-13-2012, 08:20 AM #9
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,550
-
10-14-2012, 08:30 PM #10
Interlock your pump with the flow switch and set up a freeze protection. I don't guess it wouldn't much matter what controls you use. As far as staging goes, looks like x controls will just bring on more compressors in order to compensate for the load. Good stuff.
Last edited by txhvac; 10-14-2012 at 08:34 PM. Reason: Wrong spelling
Sic Semper Tyrannis.
-
10-14-2012, 10:22 PM #11
Professional Member
- Join Date
- Nov 2005
- Location
- Shreveport, Louisiana
- Posts
- 2,255
So you are looking at 9 binary outputs, 2 binary inputs, 5 analog inputs, 1 analog output. Are you isolating the heat exchangers from each for low load conditions? Did you provide head pressure controls on the condensing units? How about a flow meter instead of DP?
UA Local 141
-
10-15-2012, 06:32 PM #12
New Guest
- Join Date
- Oct 2012
- Location
- Israel
- Posts
- 4
4 stage control + fan
The fan contact will run the water pump. Hopefully the condensing units are equipped with essential safety
devices and solenoid valves( not essential in this kind of a system). Make sure the the pump
is off delayed. Cheers
-
10-15-2012, 10:00 PM #13
Professional Member
- Join Date
- Nov 2005
- Location
- Shreveport, Louisiana
- Posts
- 2,255


Reply With Quote