    Hello. Since having a new control board installed in my 25 year old carrier furnace,I notice after the burner kicks off,the motor only runs for about a minute and a half,then stops. There is still hot air coming out of the registers.It seems to me it should run a little longer. Is this adjustable? Thanks so much for any info. GREAT SITE !!

  2. #2
    Join Date
    Dec 2002
    Location
    Rochester, MN
    Posts
    5,304
    25 years old?? I am not aware of any furnace that old having a board controling the fan off time.

    most boards has a setting for fan off delay, sounds like yours need to changed. If the board has nothing, and like most older furnace, there is a fan limit-control.

  3. #3
    Thanks for the reply,mayguy. I guess I ment the circuit board,not the control board.Is the fan delay part of this NEW board the tech installed ? I paid $400.00 for it,and I hope it is adjustable!! The fan stops running with the register temp of 106 degrees.seems like a waste of hot air left in the registers .thanks again.

  4. #4
    Join Date
    Jul 2002
    Location
    Zelienople, Pa
    Posts
    2,965
    You should've put that $$$ into a new furnace...

  5. #5
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    34,079
    Probably the HH84AA020 board and it should have some adjustment to it though probably not over 2 minutes.

  6. #6
    Your right,baldloonie. The hh84020 board was replacd,and then my problem started. I just couldn`t see throwing out my furnace because of a sticking heater fan relay,bschvac,but I would of never guessed it would be so expensive. So you say this is adjustable ?? Thanks for the reply !!

  7. #7
    Join Date
    Jul 2002
    Posts
    962
    Why don't you call the tech who installed it and ask him? He will probably come back and adjust it for you.

  8. #8
    Well,thanks for the replys. At least I know there is an adjustment on it.

  9. #9
    Join Date
    Jan 2006
    Location
    Dayton, Ohio [USA]
    Posts
    752
    Originally posted by bluestreak
    Well,thanks for the replys. At least I know there is an adjustment on it.
    if its not working right [which it isnt] the technician should come back out and fix it for free. just call the company and tell them that you had just had the board installed and you dont think its working right.

  10. #10
    Join Date
    Apr 2004
    Posts
    7,680
    I would certainly want to know the actual temperature rise while it's running. I suspect it is high if you still have a 30+ rise a minute and a half after the burner shuts down. You may have an airflow issue all or the fan speed may not be set correctly.

  11. #11
    Thanks for the replys,furnace-dude and docholiday.I would call the tech back out, but the board was replaced 1 year ago.Seems a little late. Should have called sooner. Air flow problem,doc ?? I did shut off the registers to 2 room since my kids moved out. Maybe I will open them back up and see what happens.I have a pretty good digital cooking thermometer Can it be used to check the temp. rise ?? thanks again. You guys ROCK !!

  12. #12
    Join Date
    Dec 2002
    Location
    Rochester, MN
    Posts
    5,304
    Yeah, take a temp reading and see what it's at just above the A/C coil, and return before the filter.

  13. #13
    Join Date
    Jan 2006
    Location
    Dayton, Ohio [USA]
    Posts
    752
    you should still have a year warranty from the instslling company. why not call and ask if it is still covered. the worst case, they would say you have to pay for them to come out.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event