Results 1 to 4 of 4
Thread: filter dryer
-
10-11-2012, 10:05 PM #1
Professional Member
- Join Date
- Jan 2007
- Posts
- 25
filter dryer
I was working on a Freezer. I found Compressor bad. replaced Compressor and filter line dryer. found liquid line dryer guts busted up. it stoped up the line befor the txv. what would cause the dryer to do that.
-
10-11-2012, 10:26 PM #2
the drier being dropped
the compressor breaking down and chunks of metal breaking apart the drier.
-
10-11-2012, 11:16 PM #3
If drier is severely restricted and then overcharged to compensate ......hydraulic liquid pressure is pretty strong.
-
10-14-2012, 10:35 PM #4
Professional Member
- Join Date
- Jan 2007
- Posts
- 25
ok the compressor did go bad. so it could have been that.


Reply With Quote