Results 1 to 4 of 4

Thread: filter dryer

  1. #1
    Join Date
    Jan 2007
    Posts
    25
    Post Likes

    filter dryer

    I was working on a Freezer. I found Compressor bad. replaced Compressor and filter line dryer. found liquid line dryer guts busted up. it stoped up the line befor the txv. what would cause the dryer to do that.

  2. #2
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    5,162
    Post Likes
    the drier being dropped

    the compressor breaking down and chunks of metal breaking apart the drier.

  3. #3
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,207
    Post Likes
    If drier is severely restricted and then overcharged to compensate ......hydraulic liquid pressure is pretty strong.

  4. #4
    Join Date
    Jan 2007
    Posts
    25
    Post Likes
    ok the compressor did go bad. so it could have been that.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.