    Weird alarms coming in, chiller will not run it. appears that there is a problem with the diagnostic board. The faults that show up keep changing along with the dates of the faults. Then the fault history will clear and start over again. All of this happens without the chiller even running. Now I am back to my original theory that it caught a stray power surge caused by the storms that went through here over the weekend.

    Any thoughts?

  2. #2
    Join Date
    Jun 2012
    Location
    so cal
    Posts
    22
    Post Likes
    check for short on a sensor or transducer. also check all ribbons and wire connections are pushed in. i just had a yt fail because of this.

  3. #3
    Join Date
    Aug 2011
    Location
    York, PA
    Posts
    185
    Post Likes
    Quote Originally Posted by chillersinc View Post
    check for short on a sensor or transducer. also check all ribbons and wire connections are pushed in. i just had a yt fail because of this.
    agree, sounds like a loose wire or connection.

  4. #4
    Join Date
    Jul 2011
    Location
    East coast USA
    Posts
    1,246
    Post Likes
    Thread Starter
    Update... I did check all connections and everything went back to working great. I cant pin point which wire or connection, but i did find a few loose. I think that was it...Thanks for the tip!!

  5. #5
    Join Date
    Apr 2012
    Location
    So.Fl. & NYC
    Posts
    151
    Post Likes
    Depending on York chiller type, there is an external box located over the cooler barrel,weather proof. Has all temp./safety wires in it,I have found rubbed/cut wiring inside giving false alarms,open it up and replace all wirenuts. Should make problems stop at once,
    With severe weather could have become wet inside.

  6. #6
    Join Date
    Jul 2011
    Location
    East coast USA
    Posts
    1,246
    Post Likes
    Thread Starter
    New issues, The system ran great for a awhile than shut down. Power down and up , screen passes dia. but the unit will not run. I see the red light on MB CR18 failure. any ideas?

  7. #7
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    The red light doesn't necessarily mean anything. The manual tells of its function. I think almost every board I've seen has the red light illuminated. Let's get specific...from the M/N it should be an Optiview panel. Is it the original microboard 031-01730-xxx? What do the two lines on the top left of the Optiview home screen say?

  8. #8
    Join Date
    Jul 2011
    Location
    East coast USA
    Posts
    1,246
    Post Likes
    Thread Starter
    00000005.jpg00000001.jpg


    check this out not sure of the last few numbers 000 or 040....

  9. #9
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    O.K., you have a 031-01730-000 board. According to the second photo you are in the local mode and service level and the system is stopped. What happens when you push the rocker switch on the panel to the start/run position? Does the system go into pre-lube? What does the screen (top two lines) say then. In the photo you've shown indicates the rocker switch is off.

  10. #10
    Join Date
    Jul 2011
    Location
    East coast USA
    Posts
    1,246
    Post Likes
    Thread Starter
    Quote Originally Posted by KnewYork View Post
    O.K., you have a 031-01730-000 board. According to the second photo you are in the local mode and service level and the system is stopped. What happens when you push the rocker switch on the panel to the start/run position? Does the system go into pre-lube? What does the screen (top two lines) say then. In the photo you've shown indicates the rocker switch is off.
    when we push to run, nothing happens. the screen stays the same.

  11. #11
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    What have you done to troubleshoot the circuit from the 120 VAC on the terminal block to and through the rocker switch? Start there and follow that path until you find out why you aren't getting power to the point of initiating a run command.

  12. #12
    Join Date
    Jul 2011
    Location
    East coast USA
    Posts
    1,246
    Post Likes
    Thread Starter
    Quote Originally Posted by KnewYork View Post
    What have you done to troubleshoot the circuit from the 120 VAC on the terminal block to and through the rocker switch? Start there and follow that path until you find out why you aren't getting power to the point of initiating a run command.
    I had a chance to visit the site and started to check that out. i will follow through. My immediate thought that it may be the switch. I will let you know. Thanks for the fast responce

  13. #13
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    Quote Originally Posted by dlove View Post
    i will follow through. My immediate thought that it may be the switch. I will let you know. Thanks for the fast responce.
    Inquiring minds want to know...what did you find?