    We have a customer who wants to convert all of his existing pneumatically controlled 3/4", 2-way steam valves in radiators to electronic for BAS control. The existing valves are mounted inside the radiators next to the elements. The pneumatic valve heads are obviously able to withstand the ambient heat generated from the steam (not sure of the ambient temperature) but we are afraid standard electronic valve actuators will fail in due time because most seem to be rated to withstand up to approx 125degF.

    Does anyone know if any high temp electronic valve/actuator assemblies are available for this application or what possibly can be done to standard electronic actuators for heat protection ?

    Thanks.

  2. #2
    Join Date
    Dec 2004
    Location
    San Francisco Bay Area
    Posts
    434
    We've had good success on radiators with Danfoss ABNM actuators (0-10VDC signal) - they are rated to 140F (I think that's enough for your application) ...not sure of the exact model of the associated valves, but this ought to point you at the options available from Danfoss: http://na.heating.danfoss.com/PCMPDF...20Brochure.pdf

  3. #3
    Join Date
    Jan 2003
    Location
    USA
    Posts
    1,287
    Belimo has a line of high temp valves also.
    Propagating the formula. http://www.noagendashow.com/

  4. #4
    Join Date
    Apr 2008
    Location
    Northeast
    Posts
    74
    Quote Originally Posted by orion242 View Post
    Belimo has a line of high temp valves also.
    I called Belimo today and the guy told me they do not have high temp valves and that their actuators are rated to 122F. Any idea on the model#. I'll double check their website. Dave, I'll look into the Danfoss valves as well. Thanks.

  5. #5
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    2,305
    I know Honeywell makes one that will be rated for your application. I'll have to see if I can get some numbers. The ones we use have 350 superheated water at 275 psi.

  6. #6
    Join Date
    Jan 2003
    Location
    USA
    Posts
    1,287
    Quote Originally Posted by NightrainATC View Post
    I called Belimo today and the guy told me they do not have high temp valves and that their actuators are rated to 122F. Any idea on the model#. I'll double check their website. Dave, I'll look into the Danfoss valves as well. Thanks.
    It's the HTCCVs.

    Apparently they only mean the valve body, wtf.... Guess I should have read the marking bs a bit closer.
    Propagating the formula. http://www.noagendashow.com/

  7. #7
    Join Date
    Apr 2010
    Location
    So Cal
    Posts
    45
    What is the reason for wanting to get rid of the pneumatic valves. It may be easier to output signal to an I2P transmitter which receives the signal from bas and converts to an pneumatic output.

  8. #8
    Join Date
    Mar 2005
    Location
    Pacific Time Zone
    Posts
    3,955
    I've used Delta valves - deltacp.com on steam radiator applications just as you are talking about and they have a material change on the shaft to help prevent the heat from transferring up to the actuator. As long as your radiator airflow isn't blocked and the actuator is mounted to the side of the radiator and not above it the actuator shouldn't see the same temps as what is leaving the radiator.
    "How it can be considered "Open" is beyond me. Calling it "voyeur-ed" would be more accurate." pka LeroyMac, SkyIsBlue, fka Freddy-B, Mongo, IndyBlue
    BIG Government = More Dependents
    http://threedevilskennel.com/ - not my website.
    Versatile Hunting Dog Federation - www.vhdf.org/


Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •