    As an older contractor, I am having a hard time with this. Obviously, manual D would not be required, but still. Only one town in my area is asking for them now, but that will change. Any advice? Manual S would be impossible as the system revs up and down.
    Thanks

  2. #2
    Join Date
    Jun 2006
    Location
    Richmond, VA
    Posts
    4,015
    Post Likes
    Manual j is required to determine the load on the structure. You can get manual j and do it long hand or get software (not sure how detailed you need to be in your area-there are easy programs and detailed ones). Manual s is equipment selection to handle the load determined in manual J. Doesn't matter if it revs up and down as long as it covers the max. load.
    I wish I had a $1.00 for every response I deleted.....

    "Decidedly Superior in a twisted pathetic way".....

  3. #3
    Join Date
    Dec 2010
    Location
    Woodbridge Twp, NJ
    Posts
    1,309
    Post Likes
    If the jurisdiction is requiring both, treat it as you would with a regular split. The manual J will give you the heat load and the manual S is simply verbage that the system is within 1/2 ton of the manual J calculation. It doesnt matter if the unit ramps up and down, you bought a 2 ton split, it's a 2 ton.