    Quote Originally Posted by tedkidd View Post
    No adjustment at the registers? You can get better registers, then avoid introducing penetrations and possible leakage points. Sounds like you have tight ducts, and youll want to keep it that way.
    Hmmm... I'll take that into consideration... don't want to run the risk of messing with already "tight ducts". I did install new Hart & Cooley registers and adjusted them down quite a bit. Amazingly, that did send more air to the back of the house and lowered the front to back delta to about 2*. But you can still hear the air coming from the registers when you're in the 2 b/r's closest to the plenum, whereas the other registers in the house are virtually silent. I was hoping dampers would silence these registers and allow them to be opened all the way. I suppose I could have FPL do another duct leak test for $30 after the dampers are installed, and if they leak too much, have FPL insist that the contractor re-seal at his expense. Most installers are also on the FPL PIC list for duct sealing and I'm guessing they don't like customers complaining about their work to FPL.

    Is there any ill-effect on the equipment by restricting airflow at the register?

  2. #28
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,366
    The only Ill effect I could see is if the ductwork is marginal to begin with. Equipment needs 400CFM per ton and efficiency suffers if it isn't there. Closing close registers raises the overall static pressure and reduces CFM and/or will make a variable speed blower work harder. Smaller equipment requires less ductwork/airflow and closing registers will have less of an effect.

  3. #29
    Join Date
    Jul 2007
    Location
    Delaware
    Posts
    3,824
    You may wish to be less vocal and descriptive about the HVAC contractors in your area. You may find it difficult to find someone who is willing to work for you.

  4. #30
    Join Date
    Feb 2006
    Location
    Float'N Vally, MS
    Posts
    1,841
    Quote Originally Posted by Florida Joy View Post
    1827sf Central Florida East Coast lots & lots of single pane sliding glass
    Why don't you consider doing something with your windows. Single pane windows are a BIG heat gain.
    Then you will get down to the 3 ton level that you want?

    BTW I live about in the same heat gain area and have a 3 ton with plenty of left over cooling ability.
    Just chec your heat gains...
    Life is too short, Behappy!
    TFMM

Page 3 of 3 FirstFirst 123

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event