low temp drop
was introduced to my new problem today. brand new unit. 2 cicuits. #1 15 degree SH and 12degree SC. #2 24degree SH and 21 degree SC. Only 10 degrees across coil. I would think #1 is OK but #2 having both high SH and SC has got me puzzled. Unit is for a gas station with a little food area. There is a hood exhaust and make up which appear to be ok. Unit never gets to set pt
-
10-10-2012, 10:57 PM #2
Restriction?
-
10-10-2012, 11:02 PM #3
Professional Member
- Join Date
- Sep 2006
- Location
- Ohio
- Posts
- 354
Sounds like ckt 2 has a restriction, look for a temp drop on the liquid line. Check the filter drier and condenser. Does it have a TXV or fixed orifices?
-
10-10-2012, 11:03 PM #4
Professional Member
- Join Date
- Feb 2004
- Posts
- 77
fixed orifice
-
10-10-2012, 11:05 PM #5
What are the pressures?
-
10-10-2012, 11:07 PM #6
Could have installed the wrong size piston in that circuit
-
10-10-2012, 11:08 PM #7
Professional Member
- Join Date
- Feb 2004
- Posts
- 77
I honestly didnt check for a restriction but havin a hard time thinkin it would cause High SH and SC
-
10-10-2012, 11:11 PM #8
Professional Member
- Join Date
- Feb 2004
- Posts
- 77
#1 135/355
#2 125/385
410 freon
-
10-10-2012, 11:13 PM #9
Professional Member
- Join Date
- Feb 2004
- Posts
- 77
47degree suction temp 95 degree liquid on circuit#1
43degree suction and 91 degreeliquid #2
-
10-10-2012, 11:20 PM #10
Professional Member
- Join Date
- Feb 2004
- Posts
- 77
could be a restriction. now that im looking at the numbers
-
10-11-2012, 06:52 AM #11
Could it be overcharged?
-
10-11-2012, 06:53 AM #12
If this is a package unit, I would weigh the charge.