It should be fantastic I admit. And it will have a good warranty. BUT. Been to 2 classes, needed continuing Ed hrs, on these things. NO WAY I'm putting my customers in bed with this. Oh ya I just installed a "warranty" coil last week. Been waiting on it for 2 1/2 months. It's not just the inverter that gives me pause. Y'all sling em for a couple years and see how they do. I hope they are fantastic. I'm gonna let your customers test em if that's OK.
-
10-11-2012, 04:50 PM #15
Florida code, ASHRAE and others suggest .2 ach when occupied. The blower door test shows .25 ACh on with an average wind and average cold weather conditions. In calm wind and moderate summer weather expect much less infiltration. Most a/c contractors say nothing. They know that the fresh air disscusion complicates the bid. If you do not care, do not expect anyone to mention it.
I brought it up because, I sell ventilation/humidity control equipment.
A fresh air change in 4-5 hours purges indoor pollutants and renew oxygen. The problem is that most a/c can not maintain <50%RH when the outdoor dew points are +55^F and low/no cooling loads without a whole house dehumidifier.
That is why it is not mentioned.How good do you want your home tobe?
Regards TBBear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
Use +Merv 10 air filter. -Don't forget the "Golden Rule"
-
10-11-2012, 06:46 PM #16
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,252
It's ALL About Windows
Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
10-11-2012, 07:20 PM #17
The infiltration rate that the blower door test came up with was not the infiltration rate that he used for the manual j you posted and the infiltration load represents 35% of your cooling load.
-
10-11-2012, 07:28 PM #18
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,252
Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
10-12-2012, 11:13 AM #19
Regular Guest
- Join Date
- Sep 2012
- Location
- Orlando, FL
- Posts
- 37
The systems they quoted were not the Greenspeed. They quoted 25HNB660A003,FV4CNB006T00,CE0501N05 from Carrier and ASZC160601B, MBVC2000AA-1A, HKT-5, TX5N4 from Amana. The 5 ton Greenspeed is crazy expensive and when you add up the cost for the zoning equipment and changing some of the duct work, you lose the cost benefit of a single system vs. 2 systems. (initial purchase) So unless it is just the cats meow and significantly more efficient and effective, I am not sure its the way to go.
Not sure what all that means, but we want the house to be good, not necessarily perfect - if there is such a thing. But we also have a budget to consider and 1st priority is repairing/sealing the ducts, sealing the holes found between the ceiling and the attic and adding additional insulation. 2nd priority is obviously replacing the current systems.
95% of the windows are double pain but not low e. We also have 6 doors that have 19 1/2 x 64" glass cut outs in them that are not double pain. Surprisingly we only have 2 windows on the south side of the house, that either are not under at least a 12" overhang, porch, etc. or shaded by trees.
-
10-12-2012, 12:11 PM #20
The blower door info says your home will not get enough fresh air unless the wind is blowing. Homes tend to leak less than blower door test indicate.
Putting a single small whole house ventilating dehumidifier in your home gets you minimal fresh filtered air during calm weather and near perfect humidity control. If you have occupants with any sensitivity to indoor air quality issues, it's important. If you want to have excellent comfort concerning humidity issues, it's important.
WHVDEH will not cost as much as a VS speed a/c which will not get you fresh air during calm weather or <50%RH during high outdoor dew points and low/no cooling loads.
To your credit, you are a concern home owner. Keep us posted on how this all works out.
Regards TBBear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
Use +Merv 10 air filter. -Don't forget the "Golden Rule"
-
10-12-2012, 01:16 PM #21
Regular Guest
- Join Date
- Sep 2012
- Location
- Orlando, FL
- Posts
- 37
Thanks for the compliment, as for the WHVDEH system, if we stay with split system, does that mean we would need 2 of these units or only need to install on upstairs system where humidity is higher and. Also if it matters, all the bedrooms are upstairs and living is downstairs, we also have a couple of large dogs that go out into the back yard quite a bit, letting in fresh air.
-
10-12-2012, 02:32 PM #22
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,252
Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
10-12-2012, 02:36 PM #23
Regular Guest
- Join Date
- Sep 2012
- Location
- Orlando, FL
- Posts
- 37
-
10-12-2012, 04:48 PM #24
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,252
The amount of tinting is measured as S OLAR H EAT G AIN C OEFFICIENT ( S.H.G.C.).
http://www.efficientwindows.org/shgc.cfm
CLEAR = 0.87
MEDIUM = 0.55
http://www.efficientwindows.org/glazing_.cfm?id=5
HEAVY < 0.30 may result in a Light Transmittance which provide such low outdoor lighting resulting in a "disturbingly dark" room even on a clear day
http://www.efficientwindows.org/city...dtype=WN&id=66Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
10-12-2012, 07:29 PM #25
If you live in the cold North, you need low-e windows that allow the winter solar heat to enter & then keep that interior radiated heat from passing back through the window pane.
On clear sunny days my furnace seldom cycles even on cold days; At 70-F indoors the design temp-difference I use is 83-F; Lacrosse, WI 99% Design is -13-F below zero. I have a 60,000-Btuh Input, 97% propane furnace that has no problem holding the design temp; - go-figure...
I only have two double pane low-e windows on the south side; one upstairs & one downstairs.
However, I have storm windows on all the other windows &, storms on the three doors.
Tight storm windows provide a u-value about equal to a double pane window at a fraction of the cost; of course they won't be low-e.