    KitControl ?
    How would you set up a "StatusEnum To StatusBoolean" conversion? I have a schedule enum coming in but i cannot get the boolean output to change when i set the schedule from occup to unoccup or vice versa.
    Connecticut
    Quote Originally Posted by gazoo View Post
    Did you set your facets and active values? If that doesn't work, you can use a boolean select.
    Aug 2008
    i have my in facets as "LonOccupancyEnum" and my active values as occupied, unoccupied...the out stays true{ok} all the time...does not change....
    Hampton Roads, Virginia
    with both occupied and unoccupied set as active when do you expect the output to be false?
    Kevin
    "There is plenty of room at the top because very few people care to travel beyond the average route. And so most of us seem satisfied to remain within the confines of mediocrity." -- Benjamin Nnamdi Azikiwe, first president of Nigeria
    "It's not the customer's job to know what they want." -- Steve Jobs
    Aug 2008
    the active value represents what???
    Connecticut
    The active values are all enum values that you want to use to set the boolean output to be active. If your schedule is 0=UNOCC and 1=OCC, set the active values to be 1 only. Then anything other than a value of 1 will result in an output of false.
    Aug 2008
    thanks man......lots of sense now.....help manual in docs is very cryptic....
    Jan 2010
    We simply take the Schedule into a boolean select and define outputs of select.
    Melbourne
    kitControl/conversions/StatusEnumToStatusBoolean.
    ...why not use a schedule/EnumSchedule and set the Schedule Facets to use the Frozen Enum for lonOccupancyEnum?