    KitControl ?
    How would you set up a "StatusEnum To StatusBoolean" conversion? I have a schedule enum coming in but i cannot get the boolean output to change when i set the schedule from occup to unoccup or vice versa.
    Connecticut
    Quote Originally Posted by gazoo View Post
    Did you set your facets and active values? If that doesn't work, you can use a boolean select.
    Aug 2008
    i have my in facets as "LonOccupancyEnum" and my active values as occupied, unoccupied...the out stays true{ok} all the time...does not change....
    Hampton Roads, Virginia
    with both occupied and unoccupied set as active when do you expect the output to be false?
    Kevin
    "Profit is not the legitimate purpose of business. The legitimate purpose of business is to provide a product or service that people need and do it so well that it's profitable."
    James Rouse
    Aug 2008
    the active value represents what???
    Connecticut
    The active values are all enum values that you want to use to set the boolean output to be active. If your schedule is 0=UNOCC and 1=OCC, set the active values to be 1 only. Then anything other than a value of 1 will result in an output of false.
    Aug 2008
    thanks man......lots of sense now.....help manual in docs is very cryptic....
    Jan 2010
    We simply take the Schedule into a boolean select and define outputs of select.
    kitControl/conversions/StatusEnumToStatusBoolean.
    ...why not use a schedule/EnumSchedule and set the Schedule Facets to use the Frozen Enum for lonOccupancyEnum?