braze mini-split vs flare connections ?
About to do first mini-split. Have done split units and always N2 fill and braze.
Approach envisioned for mini-split (410A) is to cut the flare connections off and 15% Ag silphos braze, adding a bidirectional filter dryer and moisture indicator in the process.
Opinions? Is this a wasted effort -- e.g. do mini-split flare connections have a good track record.
Last flare I used on HP (R22) was on a 7.5T carrier HP 30 years ago and was not happy.
-
10-08-2012, 11:50 PM #2
The exv on minisplits are very small and the smallest piece of trash will make it malfunction. A drier is not recommended either, they are critical charge units and a drier can make it malfunction. best to use flares for mini splits and not risk screwing it up. Read and follow manufacture reccomended procedures IMO
-
10-08-2012, 11:52 PM #3
The few I have done I've always cut and flared them because thats what I've been told from a mr. slim class.
They don't want any brazing due to risk of oxidation and contaminants because there is small strainers in the units. BUT if you flow nitro I don't see an issue but that's my 2 pennies.
-
10-09-2012, 12:11 AM #4
DO NOT install a drier on the lines. if you braze and purge nitro you will be fine with your method.
The company I'm at uses all hard pipe and fittings with these units. nitro purge is a most when brazing.
-
10-09-2012, 07:41 AM #5
have always used the flare fittings, only one failure i can remember was years ago on a sanyo unit when the flare nut split.
-
10-09-2012, 07:44 AM #6
Professional Member*
- Join Date
- Oct 2012
- Location
- Toronto, Ontario
- Posts
- 67
i have gone to a few Fujistu courses and they have said if you weld the warranty is voided
-
10-09-2012, 07:59 AM #7
Professional Member
- Join Date
- May 2010
- Location
- Oxford, UK
- Posts
- 253
If its a wall mount i usually cut them off and braze them, then you've only got flares on the outdoor unit where its easy to check, the pipes are then easier to run through a wall or behind the unit without the bulk of the nuts etc. But it depends on the make, some units have little straines just after the flares so you can't cut these.
No driers or sightglass, its an expansion line not a liquid line. Insulate both lines or it'll sweat. Measure the lineset as you go, and calculate the charge by the oz per foot/grams per meter chart, can't use subcool superheat with these.
Best advice i had when starting to fit these is read the instruction before you start, they often bring out slightly different models or change the spec etc and it will catch you out otherwise.
-
10-09-2012, 11:21 PM #8
we have a city multi going on now, 19 Ah and flares on everything
thats the main Bc controller, theres also a sub bc controller, Alot of flaring!! i feel like a pro at flaring now
. make sure you have the right flare tool and oil your tool and copper while flaring. The less brazing you do the better, nito is a must if you have to. No driers or sight glasses. They dont want brazing bc the system dosent have diers and driersshouldnt be installed
(((PEACE IS THAT BRIEF MOMENT IN HISTORY WHERE EVERYBODY STANDS AROUND RELOADING)))
(((YOU SEE A SIX PACK, I SEE A SUPPORT GROUP)))
-
10-13-2012, 11:37 PM #9
Holy hell thats one big POS just like the rest of the jap systems.
We just did a couple Panasonic Eco I VRF systems, 2 condensers and 22 indoor units on one reefer circuit.. All brazed pipe on the mains, suction, hot gas, and liquid, solenoid boxed were brazed as well but flared connections at the indoor unit.
-
10-14-2012, 09:38 AM #10
YES . The bad part is i came onto the job after they "flared everything" and the forman on the job is never there, riding the clock. Well me and another guy ended up pulling every unit off the wall and reflaring, also a bunch on the bc controller. its was a nightmare!! ive been playing cleanup on that job for 3 weeks. We got 600 lbs of nito in it thursday, SURE HOPe its all in there monday!
The moral of the story is make sure you are flaring properly and you shouldnt have a problem, good rule of thumb is about a nickels width of copper stubbed out on your flaring block, and oil while flaring and on your flare nuts while tightening, and a torque wrench you should be good to go. theses guys didnt even have a torque wrench when i got there
Last edited by david912; 10-14-2012 at 09:55 AM.
(((PEACE IS THAT BRIEF MOMENT IN HISTORY WHERE EVERYBODY STANDS AROUND RELOADING)))
(((YOU SEE A SIX PACK, I SEE A SUPPORT GROUP)))
-
10-09-2012, 11:37 PM #11
flares only, no flames on minis!!!!!!
I have not seen that it voids warranty, but makes sense.
they are trying to idiot proof the install.
have not had a failed flare in our company, that I am aware of, in the approximately 400 units installed by us.If Guns Kill People, Do Pencils Misspell Words?
http://www.youtube.com/watch?feature...&v=2kX_3y3u5Uo
http://www.youtube.com/watch?v=JVAhr4hZDJE
http://www.youtube.com/watch?v=-TC2xTCb_GU
-
10-12-2012, 10:27 PM #12
Professional Member
- Join Date
- Oct 2012
- Location
- Torrington CT
- Posts
- 70
i went to a city multi class they said to flare only no brazing they want a presser test up to 600 psi on there system and oil tool and copper
-
10-12-2012, 11:29 PM #13
We flare everything except on the branches that we run multiple heads on one branch. Where they tee off I flowed nitro and brazed them. Yes, pressure test at 600 psi for 24 hours. Then hold <500 microns for 24 hours.
To the OP, make a good flare and it will be just as good as any braze joint. When people have trouble with flares, it is invariable due to a poorly made flare.