Thread: ignition module troubleshoot
-
10-08-2012, 11:40 AM #1
Professional Member
- Join Date
- Feb 2010
- Location
- Milwaukee, WI
- Posts
- 58
ignition module troubleshoot
Carrier
M# 58GS050-EB
S#58GS-050-161EB
Owner call me to take a look at his furnace. He said he have been turning the power switch off and on to reset the system when the furnace wont recycle. I took a look at it on start up and electronic igniter will spark and lit the pilot but the igniter will not shut off until 20 minutes later. Polit will stay on for about 1-2 minute before the burner are lit. So my question is " is the ignition moduel faulty? or is there a flame sensor and is it faulty?
-
10-08-2012, 11:55 AM #2
If the igniter acts as a flame sensor, maybe it's failing. That must be an old furnace, some of those had a three wire pilot which had a bimetal strip that turns on the main burner when it gets hot enough to turn on the power to the gas valve.
-
10-08-2012, 12:03 PM #3
Professional Member
- Join Date
- Feb 2010
- Location
- Milwaukee, WI
- Posts
- 58
yes it does have a three wire.. is there any way for me to test it?
-
10-08-2012, 12:06 PM #4
I don't know of any way to test it, but I would start with cleaning the pilot burner and pilot orifice.
-
10-08-2012, 01:05 PM #5
If you replace the 3 wire pilot, dont use the Robert Shaw after market brand, use OEM...the RS's fail in about a year. Someone posted the proper way to check a 3 wire pilot a few years back...might want to do a search on the topic.
After the pilot flame is lit on the 3WP, it heats up a bimetel switch that closes the circuit for the main valve. I believe they both stay on until the heat is satisfied?....been a while.
A good indication of a bad 3WP is the main burners dropping out and coming back on. Proven by seeing the voltage drop out to the MV useing your meter."If anybody can draw on the power, where do we put the meter?" - JP Morgan before pulling Tesla funding
-
10-08-2012, 01:09 PM #6
Regular Guest
- Join Date
- Jun 2011
- Location
- Detroit vicinity, Michigan
- Posts
- 79
Once the pilot is lit you can unplug the harness, then jumping out two of the pins on the harness will bring on main flame.....problem is I can't remember which two without seeing the diagram, but yellow to green seems to sound familiar.
I give those pilots 1 to 2 minutes Max to make the switch and those warp switches tend to stick....90% of the time its just a dirty pilot orifice, but usually end up replacing it to prevent a callback.
-
10-08-2012, 01:26 PM #7
Send me an email (address is in my profile) and I will send you the manuals on this unit, and info on troubleshooting this 3 wire pilot.
I don't post technical info, or manuals, in this "OPEN" forum.
Also, that is not the correct serial number. Looks like a product number.Last edited by rundawg; 10-08-2012 at 01:43 PM.
Instead of learning the tricks of the trade, learn the trade.
-
10-08-2012, 01:29 PM #8
Professional Member
- Join Date
- Feb 2010
- Location
- Milwaukee, WI
- Posts
- 58
mmm ok ill give it a try, but that does not explain the owner telling me the furnace wont kick back on after a couple of cycle. He have to reset the whole furnace.
-
10-08-2012, 07:55 PM #9
Professional Member
- Join Date
- Dec 2011
- Location
- somewhere between here and there
- Posts
- 457
ok so we have decided that it has a warp switch.
if it has a warp switch, than it has a cracked htx.....have yet to come across carrier with warp switch that didnt have cracked htx....
Please, Please Please......keep the Factory Smoke in the Wires!!!!!
Is it Rum'Oclock yet???
-
10-08-2012, 08:02 PM #10
-
10-08-2012, 08:20 PM #11
The ignition modules on that machine aren't very robust either and aren easy to get.
Check the heat exchanger, near the top around where the dimples are. It may be cracked.
-
10-08-2012, 10:41 PM #12
Regular Guest
- Join Date
- Jun 2011
- Location
- Detroit vicinity, Michigan
- Posts
- 79
-
10-17-2012, 08:14 PM #13
Regular Guest
- Join Date
- Mar 2012
- Location
- Sandy Springs ,Ga
- Posts
- 12
most electronic ignition modules will lockout if flame not sensed after a set period of time ... with out knowing all the facts , it sounds like it is locking out , thats why you have to reset it ... secondly if it is igniting for 20 mins that is also an issue it should lock out much sooner than that about 30 secs to one minute max off the top of my head. ... you don't want chamber filling with gas ,,, the boom effect ... as one of the posts suggest get the manuals the answers and trouble shooting procedures you seek should be there .. good luck