    ignition module troubleshoot

    Carrier
    M# 58GS050-EB
    S#58GS-050-161EB

    Owner call me to take a look at his furnace. He said he have been turning the power switch off and on to reset the system when the furnace wont recycle. I took a look at it on start up and electronic igniter will spark and lit the pilot but the igniter will not shut off until 20 minutes later. Polit will stay on for about 1-2 minute before the burner are lit. So my question is " is the ignition moduel faulty? or is there a flame sensor and is it faulty?

  2. #2
    Join Date
    Dec 2002
    Location
    Houston,Tx.
    Posts
    16,000
    If the igniter acts as a flame sensor, maybe it's failing. That must be an old furnace, some of those had a three wire pilot which had a bimetal strip that turns on the main burner when it gets hot enough to turn on the power to the gas valve.


    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards". - Vernon Law

    "Never let success go to your head, and never let failure go to your heart". - Unknown

  3. #3
    Join Date
    Feb 2010
    Location
    Milwaukee, WI
    Posts
    62
    yes it does have a three wire.. is there any way for me to test it?

  4. #4
    Join Date
    Dec 2002
    Location
    Houston,Tx.
    Posts
    16,000
    I don't know of any way to test it, but I would start with cleaning the pilot burner and pilot orifice.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards". - Vernon Law

    "Never let success go to your head, and never let failure go to your heart". - Unknown

  5. #5
    Join Date
    Mar 2004
    Location
    SE Michigan
    Posts
    17,940
    If you replace the 3 wire pilot, dont use the Robert Shaw after market brand, use OEM...the RS's fail in about a year. Someone posted the proper way to check a 3 wire pilot a few years back...might want to do a search on the topic.

    After the pilot flame is lit on the 3WP, it heats up a bimetel switch that closes the circuit for the main valve. I believe they both stay on until the heat is satisfied?....been a while.

    A good indication of a bad 3WP is the main burners dropping out and coming back on. Proven by seeing the voltage drop out to the MV useing your meter.
    Behind the ostensible government sits enthroned an invisible government owing no allegiance and acknowledging no responsibility to the people.

    Theodore Roosevelt

  6. #6
    Join Date
    Jun 2011
    Location
    Detroit vicinity, Michigan
    Posts
    79
    Once the pilot is lit you can unplug the harness, then jumping out two of the pins on the harness will bring on main flame.....problem is I can't remember which two without seeing the diagram, but yellow to green seems to sound familiar.

    I give those pilots 1 to 2 minutes Max to make the switch and those warp switches tend to stick....90% of the time its just a dirty pilot orifice, but usually end up replacing it to prevent a callback.

  7. #7
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    5,575
    Send me an email (address is in my profile) and I will send you the manuals on this unit, and info on troubleshooting this 3 wire pilot.

    I don't post technical info, or manuals, in this "OPEN" forum.

    Also, that is not the correct serial number. Looks like a product number.
    Last edited by rundawg; 10-08-2012 at 01:43 PM.
    Instead of learning the tricks of the trade, learn the trade.

  8. #8
    Join Date
    Feb 2010
    Location
    Milwaukee, WI
    Posts
    62
    mmm ok ill give it a try, but that does not explain the owner telling me the furnace wont kick back on after a couple of cycle. He have to reset the whole furnace.

  9. #9
    Join Date
    Dec 2011
    Location
    somewhere between here and there
    Posts
    478
    ok so we have decided that it has a warp switch.

    if it has a warp switch, than it has a cracked htx.....have yet to come across carrier with warp switch that didnt have cracked htx....


    Please, Please Please......keep the Factory Smoke in the Wires!!!!!


    Is it Rum'Oclock yet???

  10. #10
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,588
    Quote Originally Posted by rundawg View Post
    Send me an email (address is in my profile) and I will send you the manuals on this unit, and info on troubleshooting this 3 wire pilot.

    I don't post technical info, or manuals, in this "OPEN" forum.

    Also, that is not the correct serial number. Looks like a product number.
    I'd be interested in that, never heard of a 3 wire pilot unless that's a regional thing?


    Sent from my iPhone using Tapatalk

  11. #11
    Join Date
    Feb 2010
    Location
    Calgary, Alberta
    Posts
    1,107
    The ignition modules on that machine aren't very robust either and aren easy to get.
    Check the heat exchanger, near the top around where the dimples are. It may be cracked.

  12. #12
    Join Date
    Jun 2011
    Location
    Detroit vicinity, Michigan
    Posts
    79
    Quote Originally Posted by rundawg View Post
    Send me an email (address is in my profile) and I will send you the manuals on this unit, and info on troubleshooting this 3 wire pilot.

    I don't post technical info, or manuals, in this "OPEN" forum.
    Point noted.

  13. #13
    Join Date
    Mar 2012
    Location
    Sandy Springs ,Ga
    Posts
    12
    most electronic ignition modules will lockout if flame not sensed after a set period of time ... with out knowing all the facts , it sounds like it is locking out , thats why you have to reset it ... secondly if it is igniting for 20 mins that is also an issue it should lock out much sooner than that about 30 secs to one minute max off the top of my head. ... you don't want chamber filling with gas ,,, the boom effect ... as one of the posts suggest get the manuals the answers and trouble shooting procedures you seek should be there .. good luck

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event