We recently had an "Energy Expert" come through the plant to do a survey. He told us that instead of running one 75hp cooling tower fan at 90% we should run three at 30% and our total load would go from 56kw to 2kw. We have some excellent control tech and a top of the line BAS. He says the system can be programmed to perform this load spreading automatically and that we would get these big savings. I have a hard time believing this. Is this a standard practice? thanks. km