    For what it's worth, here's the manual for the TSF:

    Turbo Air TSF Service Manual

  2. #15
    Join Date
    Mar 2007
    Location
    pittsburgh, pa
    Posts
    535
    Quote Originally Posted by primmers View Post
    is there two different sized cap tubes and this is the reason for the "sleeve?

    can i get a link to the above??
    According to this:

    http://www.turboairinc.com/Refrigera...sureChart.aspx

    It looks like the length that runs through the box ( I believe 90.55 is the length, unable to find any info from our last battle with a TA freezer) is the same id, but the length and id before the sleeve varies depending on the compressor.

    The 3 door TA freezer(tsf-72d) that gave my boss all sorts of trouble earlier in the year ended up getting a TXV and a receiver (then we found the defrost heater would intermittanty stick on due to a bad board and may have worked with changing the cap tube from the drier to the sleeve).


    Now, I did not care for mounting the sensing bulb to the accumulator, and had to play with the superheat due to excessive txv hunting but,knock on wood, it has been working well.

    I have been unable to find any of our notes regarding cap tube sizing or txv info due to someone "just being a little bit cranky" due to all the unbillable hours wasted on this thing.

    You might be able to find the cap tube size from the "order online" section and run a new suction line/cap tube up over the top of the box into the evap area.

    Good luck.

  3. #16
    Join Date
    May 2005
    Posts
    1,347
    thanks icemeister..and 76olds, ill buy the unit from my customer before going through all that...

  4. #17
    Join Date
    Mar 2007
    Location
    wedged in freezer shelf
    Posts
    6,542
    So they are trying to make one size fits all cabinets and bolt on specific C/U's ? ....... Good Grief
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  5. #18
    Join Date
    May 2008
    Location
    South Florida
    Posts
    58
    Quote Originally Posted by trippintl0 View Post
    We typically run a new cap tube up the back wall, drill a hole through the box, and then silicone the penetration afterwards, its actually not too bad. I've done it on several True's but never on a TurboAir.

    Another way without penetrating the box: Drill a hole in the suction line by the evaporator. Cut the suction line by the condensing unit. Feed the cap. tube down the suction line. Solder it all back together. New cap tube, better subcooling and no penetration through the box.

  6. #19
    Join Date
    May 2005
    Posts
    1,347
    heres an update..today i went back to the case,i took a turner torch and heated up the cap tube going into the evaporator and around the sleeve...it still ran in a vacuum..so i cut the sleeve out, and psi tested the cap tube both ways..it blew clear..so i reassembled it, pulled a vacuum and recharged it..its running.
    i told the customer that was a freebee..but left him the invoice for the original compressor install...im going to light some candles at a catholic church for this thing, at least until i get paid..

  7. #20
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    2,845
    Quote Originally Posted by primmers View Post
    heres an update..today i went back to the case,i took a turner torch and heated up the cap tube going into the evaporator and around the sleeve...it still ran in a vacuum..so i cut the sleeve out, and psi tested the cap tube both ways..it blew clear..so i reassembled it, pulled a vacuum and recharged it..its running.
    i told the customer that was a freebee..but left him the invoice for the original compressor install...im going to light some candles at a catholic church for this thing, at least until i get paid..
    Why would he pay you for the compressor when he can go buy another used freezer from auction for cheaper?

  8. #21
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    3,077
    Quote Originally Posted by primmers View Post
    after i did the work i told the customer
    to never call ME again on this pile!
    Oh we've all had units gone bad and were married to until it worked right. I can think of a few
    I hope I never hear about again ....

  9. #22
    Join Date
    Dec 2009
    Posts
    14
    Quote Originally Posted by FSE_ View Post
    Another way without penetrating the box: Drill a hole in the suction line by the evaporator. Cut the suction line by the condensing unit. Feed the cap. tube down the suction line. Solder it all back together. New cap tube, better subcooling and no penetration through the box.
    I've never imagined that, but WOW, you must be an smart old man! I like your idea, not for this specific app, but this will be of good use when time calls. I like to make that hole in the wall and run with it. Nevertheless, I like your imagination, that's what I call engineering!

  10. #23
    Join Date
    Jun 2003
    Location
    Tampa Bay, FL.
    Posts
    119
    Quote Originally Posted by FSE_ View Post
    Another way without penetrating the box: Drill a hole in the suction line by the evaporator. Cut the suction line by the condensing unit. Feed the cap. tube down the suction line. Solder it all back together. New cap tube, better subcooling and no penetration through the box.
    Some vending machine manufacturers do that from the factory. Definitely get good sub cooling that way!

  11. #24
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    4,509
    Quote Originally Posted by FSE_ View Post
    Another way without penetrating the box: Drill a hole in the suction line by the evaporator. Cut the suction line by the condensing unit. Feed the cap. tube down the suction line. Solder it all back together. New cap tube, better subcooling and no penetration through the box.
    What about the chance of copper shavings getting into the system and causing another restriction?
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  12. #25
    Join Date
    Mar 2007
    Location
    wedged in freezer shelf
    Posts
    6,542
    For replacement I've used a tee at either end to route the cap out of the suction instead of drill before. It was such a PITA on one of these with the tight bends in the wall it is much easier and faster to just run a new suction/cap heat exchanger up

    FWIW I believe I saw a small mani ice maker that ran the cap inside the suction
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  13. #26
    Join Date
    May 2005
    Posts
    1,347
    Quote Originally Posted by KB Cool View Post
    Why would he pay you for the compressor when he can go buy another used freezer from auction for cheaper?

    because it was the customers wish to have it replaced..

Page 2 of 3 FirstFirst 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event