    Jumping out Lennox gcs11 953 250

    Doing pm on rtu's. I came across 4 older Lennox rtu's gcs11. Not sure how to jump these out. From the looks of it dc voltage is run into a control panel and then over to another panel in comp section to what is labeled A1 logic panel. This controller has terminals labeled sen,stat,24vac,econo,and heat cool at top. Not sure where I would be able to jump this unit to test. Schematic not helping. I am use to seeing terminal strip with r y w g etc

  2. #2
    Join Date
    Aug 2012
    Posts
    1,518
    It sould have a test pin or something of that nature to run through the cycles, don't quote me though.

  3. #3
    Join Date
    Jun 2006
    Location
    New Jersey
    Posts
    4,092
    If you pull the stat wires off the logic panel. Terminals 1-5. Then if you jump terminal 2 to 5, all heat stages will run. If you jump terminal 2 to 4, all cool stages will run.

    Here's the pdf for you....
    Attached Images Attached Images

  4. #4
    Join Date
    Jul 2007
    Posts
    70

    Smile Simulator

    THe simulator is the best option for servicing the w-973 panel.

  5. #5
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    2,739
    How can you do a PM without cycling the unit from the t-stat? T-stat is part of the system.
    Local 597 Service Fitter
    Metal Trade Journeyman

    PAY ME NOW OR PAY ME LATER

    It was working when I left...
    WWFD

  6. #6
    Join Date
    Jul 2007
    Posts
    65
    Quote Originally Posted by ascj View Post
    If you pull the stat wires off the logic panel. Terminals 1-5. Then if you jump terminal 2 to 5, all heat stages will run. If you jump terminal 2 to 4, all cool stages will run.

    Here's the pdf for you....
    Thanks asjc, that information really helped.