    I currently have a Tempstar ntc6075 and went to start up without any reaction. Check 110v to the circuit board...ok Checked 24v from transformer....ok I have both to the control board and still nothing. I have also checked all limits and pressure switch. Limits are closed and PS will close on start up. What else have I missed?????

    [Edited by biggdaddy47 on 10-14-2006 at 06:37 AM]

  2. #2
    Join Date
    May 2003
    Location
    Dixie
    Posts
    1,344
    Post Likes
    "What else have I missed?????"

    training, experience, knowledge.....

    are you a tech or H/O?

  3. #3
    Join Date
    Oct 2006
    Posts
    3
    Post Likes
    I am a home owner with some electrical skill. All indications after my checks would point to the control board...

  4. #4
    Join Date
    May 2006
    Location
    east central indiana
    Posts
    1,117
    Post Likes
    Betcha this furnace has a SmartValve don't it?

  5. #5
    Join Date
    Jan 2004
    Posts
    139
    Post Likes
    Hey, don't diss smart valves. They are great.

    I have only replaced them on about 99.9% of the Tempstar furnaces I installed with a smart valve. Some of them 2 to 3 times in one year.

  6. #6
    Join Date
    Oct 2006
    Location
    The Beach
    Posts
    775
    Post Likes

    Furnace will not come on.

    I Have been putting on a stronger transformer and this will open the Smart gas valve.
    Blue Fox

  7. #7
    Join Date
    Jan 2004
    Posts
    139
    Post Likes
    Every smart valve I have replaced was due to the fact that it would not start the inducer motor.

  8. #8
    Join Date
    Oct 2006
    Posts
    3
    Post Likes
    yea this furnace has a "dumb valve" on it. the original transformer I also had to replace because it started smoking. If I get another stronger transformer and replace the valve, would this take care of my problem? Thanks.....

  9. #9
    Join Date
    Apr 2006
    Location
    South West Ohio
    Posts
    415
    Post Likes
    and to think. Honeywell reports that 90 to 95% of the smart valves they get back under warrenty are NOT bad.

    To think Tempstar had to "dumb" the furnace down so the techs could work on it properly.

  10. #10
    Join Date
    Jan 2004
    Posts
    139
    Post Likes
    It's funny how they lay blame on the techs.

    None of the furnaces worked before replacing the valve but they all worked after. Imagine that!