    Type of extra filter needed with Electronic air cleaner?

    Hello,
    I have a 3 ton heat pump with an electronic air cleaner. Before the return air enters the electronic air cleaner there is a 1/4" aluminum mesh screen, and after the air cleaner I have been using the 1" pleated style MERV 8 filter. To maximize air flow I am considering replacing the pleated style filter with a cheap fibreglass filter with no MERV rating; my thinking being that an electronic air cleaner plus a 1" pleated MERV 8 is overkill. Mostly I want to maximize air flow, but I also don't want to develop a dirty coil. What do you guys think? Great forum by the way, long time lurker, first time poster!

  2. #2
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    6,736
    You shouldn't need anything more than the prefilter (aluminum) and the EAC cells as long as clean should catch most particles and keep the coil clean. Any other filter is not benefitting and is putting a strain on your system that will likely cause premature failure of compressor and/or heat exchanger.

  3. #3
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,728
    ditch the EAC cells and install a 5" media filter in their place.

    you can tell by how dirty the merv8 gets how much dust is getting through the EAC.

  4. #4
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,060
    Quote Originally Posted by t527ed View Post
    ditch the EAC cells and install a 5" media filter in their place.

    you can tell by how dirty the merv8 gets how much dust is getting through the EAC.
    I agree if you want to keep the coil clean. The velocity of your return would need to be around 250 to 275 feet per minute for the EAC to perform as designed. Unfortunately most returns are way undersized causing velocities in the 700 to 1000 fpm range causing excess noise and filter issues.

  5. #5
    Join Date
    Oct 2012
    Location
    Toronto, Ontario
    Posts
    67
    This is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise here. Please apply to the AOPC today, thank you.

    You can find the rules for posting and qualifications here.

    Further infractions may result in loss of posting privileges.
    Last edited by beenthere; 10-09-2012 at 03:47 PM. Reason: Non Pro * Member

  6. #6
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    2,037
    I would either put in a media filter or keep the 1" pleat after the EAC.

    When large particles go through an EAC they become electrically charged. When they get close to the collection cell often times they throw a spark that incinerates the particle. The charge is then disipated so the ash has no charge. It then passes through the collection cell. This is why you need the post filter.

  7. #7
    Join Date
    Aug 2012
    Posts
    2,643
    media filter instead of EAC would be a better option.