    Which vacuum gauge is right?

    A few days ago a co-worker and I got to do a evaporator coil and condenser coil changeout under warranty, due to the original coils leaking. Both of us are tool-aholics and we wanted to compare vacuum gauges.
    Our vacuum setup included: fresh vacuum oil, Appion 3/8 x 1/4 hoses, Appion CRT's, standard 6 cfm vacuum pump, Yellowjacket vacuum tree at pump and all fittings with Nylog.
    This is about 20 mins in.
    My Bluvac never dropped below 1000 microns picture shows at 1037 microns. His JB held steady within the 270 range. Now being that the system was mainly new and only 2 places for oil and products of old refrigerant to stick around were compressor and lineset. Which gauge is right? We weren't expecting exact #'s but something within a ballpark.
    We had a 3rd micron gauge a Fieldpiece and it was down in the 400 range.
    What do you guys think?
    Attached Images Attached Images  
    Any fool can know. The point is to understand. Albert Einstein

  2. #2
    Join Date
    Dec 2007
    Location
    dealemd
    Posts
    78
    Post Likes
    how long did u let it sit to equalize,,, when pullin down the larger suc side line will take longer

  3. #3
    Join Date
    Mar 2007
    Posts
    3,824
    Post Likes
    Where was the vacuum pump in relation to both gauges? Was it running at the time of the picture? I haven't found a digital gauge that I trust yet.
    Don't pick the fly crap out of the pepper.

  4. #4
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,817
    Post Likes
    Was the JB on the liquid side or right on the vacuum tree near the vacuum pump? Thats far away from the spot where the BluVac was. I wouldn't expect the JB to show what the BluVac shows anyways since it is a ±5% of reading thru the entire operating range and the JB is probably more like ±20% in a small temp. range. They work best on a hot day. Use it on a cooler day and its worse IMO. The JB is so bad they dont even publish its accuracy. I love its giant display though.
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  5. #5
    Join Date
    Jun 2007
    Location
    Jersey
    Posts
    201
    Post Likes
    Thread Starter
    Parttime59..... the system is open for the pump in this picture. When we did allow to equalize Bluvac rose about 200 microns. JB held steady within a few microns.

    TechRob...... We had to 2 Appion 3/8 x 1/4 hoses coming off the YJ tree that was on the pump. Hope that answers your question. Yes pump running and system open to pump.

    itsiceman.... JB was on bull of Appion CRT on liquid line. Bluvac on bull of Appion CRT on suction line. Top of YJ tree was capped off.
    Any fool can know. The point is to understand. Albert Einstein

  6. #6
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,817
    Post Likes
    I think if someone did a demonstration with some oil at various states in vacuum display like they have in science classes it would be easy to see why you did not go below 1000 microns on the BluVac in twenty minutes and show why you get the rise you see. It would also prove most the other gauges out there as not the same as a BluVac. IMO in twenty minutes your vacuum pump oil is just warming up on a cool day.
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  7. #7
    Join Date
    Dec 2003
    Location
    Citrus County, Florida
    Posts
    3,341
    Post Likes
    You should have the micron guage pointing upward so it does not get oil logged. The Blue-vac appears to be pointing downward. I would clean it with alcohol.
    Last edited by Gunslinger; 10-07-2012 at 02:11 PM. Reason: typo
    Doug

  8. #8
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,381
    Post Likes
    Id like to see another one in the equation. Like a yj

    Sent from my HTC Sensation 4G using Tapatalk 2

  9. #9
    Join Date
    May 2010
    Location
    Canada
    Posts
    1,224
    Post Likes
    I have used the Supco, the yellow jacket, inficon, cps, the Jb, and the UEI ( same as bluvac).

    I trusted the JB the least and the UEI the most. Then JB would read 5000 microns when open to atmosphere.

  10. #10
    Join Date
    Feb 2010
    Location
    Calgary, Alberta
    Posts
    1,679
    Post Likes
    Quote Originally Posted by eddiegoodfellar View Post
    I have used the Supco, the yellow jacket, inficon, cps, the Jb, and the UEI ( same as bluvac).

    I trusted the JB the least and the UEI the most. Then JB would read 5000 microns when open to atmosphere.
    My supco does that sometimes. Don't know what's wrong, but everytime I use it beside the YJ it works correctly and reads the same, if only delayed a little.

  11. #11
    Join Date
    Jan 2005
    Location
    Akron
    Posts
    1,815
    Post Likes
    One thing to consider is if you were really leak tight. The Blu-vac will respond to any leaks much faster then most other vacuum gauges. If you had any leaks near the connections that gauges would read differently. About that only way to do what you are trying to do is to have everything hooked to the same connections and the same point on the system.
    JLB,

  12. #12
    Join Date
    Apr 2008
    Location
    Central CA
    Posts
    567
    Post Likes
    It sounds like the system wasn't blanked off from the pump, so now your reading at two different points in the system.
    When you blanked it off from the pump and let it stabilize what was your final readings? still above 1000 microns?

    I would grab a empty recovery tank and put both gauges on there and see how long it takes to pull down, hold, and compare the two.

    Getting use to the bluvac takes some patience, it wil make you question the vacuums you pulled in the past once you can read what its telling you.

    Did you blow out the line set real well before you hooked up the new coils?
    Typically on a new split system and line set it takes about 10-15 min to pull down below 500 and hold almost every time with a 50' line set.
    However if i have to pull a coil for cleaning and replacement it takes at least 1-2 hours most times to get a good stable reading, usually go off to another call or grab something to eat when thats taking place.

    Only difference in the between the two scenarios is the line set has been coated in oil, so longer vac times.

    Whenever i have a system that stalls out on the micron gauge i break the vac with a low pressure nitro purge to get the molecules moving along through the system and out the pump.

    Thats my experience anyway, hope it helps.

  13. #13
    Join Date
    Jan 2008
    Location
    In the work truck
    Posts
    3,275
    Post Likes
    http://www.youtube.com/watch?v=G_6iOKzAuDA

    http://www.youtube.com/watch?v=idWheO5bogQ

    http://www.youtube.com/watch?v=IeHpFOgvhY0

    I had doubt in micron gauges as well so I did some non-scientific tests. My conclusion.. THey all like to read differently.. Some are way further off then others.. In my experience that Supernova gauge is JUNK..
    Gotta have the right tool for the job!

    Where is all the stuff MADE IN THE USA?

    "Thats what we do Troy. Incredible, Invisible, Imbelivable things. We are an Unseen, Unknown, Unvincible fraternity of craftsman.."

  14. #14
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    4,439
    Post Likes
    I own the Supernova, I have compared its reading with my Thermal 14571 and they are almost identical.
    Lets see what comes next, greenvac? pinkvac?......thats going to create havoc among the zombies

  15. #15
    Join Date
    Sep 2012
    Location
    NW Louisiana
    Posts
    269
    Post Likes
    I have only the Yellow Jacket "Deluxe LED" part number 69060. I trust it. Usually anything with a thermocouple vacuum sensor is more reliable/accurate than thermistor vacuum sensors.

    http://www.yellowjacket.com/product/688

    CT

  16. #16
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,817
    Post Likes
    valdelocc How old is your DV-40? I had two DV-40's close to when they came out and they were both where a joke compared to my Thermal. I only ever saw reading in the same ballpark when to was a hot summer day.
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  17. #17
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    4,439
    Post Likes
    Quote Originally Posted by itsiceman View Post
    valdelocc How old is your DV-40? I had two DV-40's close to when they came out and they were both where a joke compared to my Thermal. I only ever saw reading in the same ballpark when to was a hot summer day.
    got it last year as a Christmas present, I'll take pictures next time I use them.

  18. #18
    Join Date
    Sep 2004
    Posts
    13,938
    Post Likes
    if i do a small res split

    i just put the micron gauge on the high side only, no hose.

    then vacuum from the suction side.

    this way i trust the micron gauge reading.

    as for which one is correct?

    who knows?
    are they both temperature compensated?
    true knowledge exists in knowing that you know nothing.

  19. #19
    Join Date
    May 2005
    Posts
    1,771
    Post Likes
    at $750 it better work....

  20. #20
    Join Date
    Sep 2004
    Posts
    13,938
    Post Likes
    what is $750???????
    true knowledge exists in knowing that you know nothing.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •