Results 1 to 13 of 16
Thread: btu math help
    Oct 2012
    btu math help
    If 11532 btu's were removed from 62 lbs of water at a 72 degrees f water temp , what would be the new temp of the water ?
    Homework Question....appreciate some help with a formula.
    Nov 2011
    Long Island, NY
    It takes 1 BTU to raise 1 pound of water 1 degree F.
    Oct 2012
    understand the definition, still confused on how to answer the question.
    Thanks for the response
    Either there is a typo here or you're getting into phase change, too.
    You're removing eleven thousand, five hundred and thirty two BTUs from sixty two pounds of water at seventy two degrees?
    I typed the full words out to prevent confusion.
    I ran a little math and this doesn't add up to a typical problem.
    Are you adding or removing heat?
    Also, moving thread to tech to tech. AOP is for equipment questions.
    Rochester NY
    Quote Originally Posted by oliesteveo View Post
    11532/62=186 per pound. 40 gets to freezing.
    How many btu to freeze a pound? probably more than 146, so I'd say new water temp 32f.
    Oct 2012
    yes sir...removing 11532 btu from 62 lbs of 72 degree f water there is a change of state latent and sensible i think
    here is another one 13080 btu were removed from 10 lbs of water at 218 degree f what would be the temp of the water
    Thanks for the help
    Thanks for the help
    water at 218???
    or STEAM at 218?
    Quote Originally Posted by tedkidd View Post
    This is it. You'll wind up with a water/ice slurry at 32 degrees.
    it will take 7440 BTU to drop the 62# from 72 to 32 (186 * 40) = 7440 This leaves 4092 extra BTUs for latent conversion
    You'll wind up with about 28# of ice by the time it's all done.
    Formula: BTU's = Lbs x Deg x SH (specific heat of material)
    Note: specific heat of water is 1.0.
    So with a little Algerbra: Btu (Lbs x SH) = Deg.
    Now to calculate Btu's required to lower temp from 72f to 32f (ICE), or 40f.
    62 lbs x 40 deg x 1 SH = 2480 btu's
    11532 - 2408 = 11408 btu's left at 32f
    Change of State - Latent heat of Fusion
    144 btu/lb to change liquid to ice : 62 lbs x 144 btu's = 8928 btus
    Now we have used : 2480 (lowering temp to 32f) + 8928 (change of state) = 11408 btus
    11532 - 11408 = 124 btus left
    Note: specific heat of ice is 0.5
    124 Btu's (62 Lbs x 0.5 SH) = 4 degs
    32f (ice) - 4f = 28f (final temperature)
    Rochester NY
    I converted to per pound because it was easier for me to follow, would have converted back at the end had I known its only 144 to ice. Guess I assumed more because there is so much energy in condensation.
    BTW, What is that exact number?
    Did not realize its 1 btu to drop ice 2 f, so would said 30 and gotten the answer wrong even knowing cost of getting to ice. Thanks for the formula and explanation on specific heat!
    Oct 2012
    change of state at 212 degrees f 970 btu at this point
    VA BCH
    I remember in physics we had a question:
    A round tub with 2' height, made of standard steel has a volume of 50 gallons at 50*, and it is filled with 15 gallons of 50*F water. How many gallons of boiling water would it take to over flow the tub, and at what temp would the water be? Answer to the nearest 0.001gal and 0.1*F.
    "The only true wisdom is in knowing you know nothing" Socrates
    Visit us at Dr. Degrees HVAC
    or like us on Facebook
    Rochester NY
    I'm sure it's not as simple as 35.001 gallons and 98.6, and am dying to see the formula...