Results 1 to 13 of 16
Thread: btu math help
-
10-07-2012, 09:08 AM #1
New Guest
- Join Date
- Oct 2012
- Posts
- 5
btu math help
If 11532 btu's were removed from 62 lbs of water at a 72 degrees f water temp , what would be the new temp of the water ?
Homework Question....appreciate some help with a formula.
Thanks
-
10-07-2012, 09:42 AM #2
Professional Member*
- Join Date
- Nov 2011
- Location
- Long Island, NY
- Posts
- 210
It takes 1 BTU to raise 1 pound of water 1 degree F.
-
10-07-2012, 09:50 AM #3
New Guest
- Join Date
- Oct 2012
- Posts
- 5
understand the definition, still confused on how to answer the question.
Thanks for the response
-
10-07-2012, 10:39 AM #4
Either there is a typo here or you're getting into phase change, too.
You're removing eleven thousand, five hundred and thirty two BTUs from sixty two pounds of water at seventy two degrees?
I typed the full words out to prevent confusion.
I ran a little math and this doesn't add up to a typical problem.
Are you adding or removing heat?
Also, moving thread to tech to tech. AOP is for equipment questions.
-
10-07-2012, 10:53 AM #5Which makes more sense to you?
CONSERVATION - turning your thermostat back and being uncomfortable. Maybe saving 5-10%
ENERGY EFFICIENCY - leaving your thermostat where everyone is comfortable. Saving 30-70%
DO THE NUMBERS! Step on a HOMESCALE.
What is comfort? Well, it AIN'T just TEMPERATURE!
Energy Obese? An audit is the next step - go to BPI.org, or RESNET, and find an auditor near you.
-
10-07-2012, 10:54 AM #6
New Guest
- Join Date
- Oct 2012
- Posts
- 5
yes sir...removing 11532 btu from 62 lbs of 72 degree f water there is a change of state latent and sensible i think
here is another one 13080 btu were removed from 10 lbs of water at 218 degree f what would be the temp of the water
Thanks for the help
-
10-07-2012, 10:58 AM #7
-
10-07-2012, 11:01 AM #8
-
10-07-2012, 11:02 AM #9
Formula: BTU's = Lbs x Deg x SH (specific heat of material)
Note: specific heat of water is 1.0.
So with a little Algerbra: Btu ÷ (Lbs x SH) = Deg.
Now to calculate Btu's required to lower temp from 72ºf to 32ºf (ICE), or 40ºf.
62 lbs x 40 deg x 1 SH = 2480 btu's
11532 - 2408 = 11408 btu's left at 32ºf
Change of State - Latent heat of Fusion
144 btu/lb to change liquid to ice : 62 lbs x 144 btu's = 8928 btus
Now we have used : 2480 (lowering temp to 32ºf) + 8928 (change of state) = 11408 btus
11532 - 11408 = 124 btus left
Note: specific heat of ice is 0.5
124 Btu's ÷ (62 Lbs x 0.5 SH) = 4 degs
32ºf (ice) - 4ºf = 28ºf (final temperature)Instead of learning the tricks of the trade, learn the trade.
-
10-07-2012, 11:23 AM #10
I converted to per pound because it was easier for me to follow, would have converted back at the end had I known its only 144 to ice. Guess I assumed more because there is so much energy in condensation.
BTW, What is that exact number?
Did not realize its 1 btu to drop ice 2 f, so would said 30 and gotten the answer wrong even knowing cost of getting to ice. Thanks for the formula and explanation on specific heat!Which makes more sense to you?
CONSERVATION - turning your thermostat back and being uncomfortable. Maybe saving 5-10%
ENERGY EFFICIENCY - leaving your thermostat where everyone is comfortable. Saving 30-70%
DO THE NUMBERS! Step on a HOMESCALE.
What is comfort? Well, it AIN'T just TEMPERATURE!
Energy Obese? An audit is the next step - go to BPI.org, or RESNET, and find an auditor near you.
-
10-07-2012, 11:32 AM #11
New Guest
- Join Date
- Oct 2012
- Posts
- 5
change of state at 212 degrees f 970 btu at this point
-
10-07-2012, 11:41 AM #12
I remember in physics we had a question:
A round tub with 2' height, made of standard steel has a volume of 50 gallons at 50*, and it is filled with 15 gallons of 50*F water. How many gallons of boiling water would it take to over flow the tub, and at what temp would the water be? Answer to the nearest 0.001gal and 0.1*F."The only true wisdom is in knowing you know nothing" Socrates
-
10-07-2012, 12:04 PM #13
I'm sure it's not as simple as 35.001 gallons and 98.6, and am dying to see the formula...
Which makes more sense to you?
CONSERVATION - turning your thermostat back and being uncomfortable. Maybe saving 5-10%
ENERGY EFFICIENCY - leaving your thermostat where everyone is comfortable. Saving 30-70%
DO THE NUMBERS! Step on a HOMESCALE.
What is comfort? Well, it AIN'T just TEMPERATURE!
Energy Obese? An audit is the next step - go to BPI.org, or RESNET, and find an auditor near you.


Reply With Quote