Page 1 of 2 12 LastLast
Results 1 to 13 of 16

Thread: btu math help

  1. #1

    btu math help

    If 11532 btu's were removed from 62 lbs of water at a 72 degrees f water temp , what would be the new temp of the water ?
    Homework Question....appreciate some help with a formula.
    Thanks

  2. #2
    Join Date
    Nov 2011
    Location
    Long Island, NY
    Posts
    210
    It takes 1 BTU to raise 1 pound of water 1 degree F.

  3. #3
    understand the definition, still confused on how to answer the question.
    Thanks for the response

  4. #4
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    20,928
    Either there is a typo here or you're getting into phase change, too.

    You're removing eleven thousand, five hundred and thirty two BTUs from sixty two pounds of water at seventy two degrees?

    I typed the full words out to prevent confusion.

    I ran a little math and this doesn't add up to a typical problem.

    Are you adding or removing heat?


    Also, moving thread to tech to tech. AOP is for equipment questions.

  5. #5
    Join Date
    Jul 2008
    Location
    Rochester NY
    Posts
    4,163
    Quote Originally Posted by oliesteveo View Post
    If 11532 btu's were removed from 62 lbs of water at a 72 degrees f water temp , what would be the new temp of the water ?
    Homework Question....appreciate some help with a formula.
    Thanks
    11532/62=186 per pound. 40 gets to freezing.

    How many btu to freeze a pound? probably more than 146, so I'd say new water temp 32f.
    Which makes more sense to you?
    CONSERVATION - turning your thermostat back and being uncomfortable. Maybe saving 5-10%
    ENERGY EFFICIENCY - leaving your thermostat where everyone is comfortable. Saving 30-70%

    DO THE NUMBERS! Step on a HOMESCALE.
    What is comfort? Well, it AIN'T just TEMPERATURE!

    Energy Obese? An audit is the next step - go to BPI.org, or RESNET, and find an auditor near you.

  6. #6
    yes sir...removing 11532 btu from 62 lbs of 72 degree f water there is a change of state latent and sensible i think
    here is another one 13080 btu were removed from 10 lbs of water at 218 degree f what would be the temp of the water

    Thanks for the help

  7. #7
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    20,928
    Quote Originally Posted by oliesteveo View Post
    yes sir...removing 11532 btu from 62 lbs of 72 degree f water there is a change of state latent and sensible i think
    here is another one 13080 btu were removed from 10 lbs of water at 218 degree f what would be the temp of the water

    Thanks for the help
    water at 218???

    or STEAM at 218?

  8. #8
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    20,928
    Quote Originally Posted by tedkidd View Post
    11532/62=186 per pound. 40 gets to freezing.

    How many btu to freeze a pound? probably more than 146, so I'd say new water temp 32f.
    This is it. You'll wind up with a water/ice slurry at 32 degrees.

    it will take 7440 BTU to drop the 62# from 72 to 32 (186 * 40) = 7440 This leaves 4092 extra BTUs for latent conversion

    You'll wind up with about 28# of ice by the time it's all done.

  9. #9
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    3,591
    Quote Originally Posted by oliesteveo View Post
    If 11532 btu's were removed from 62 lbs of water at a 72 degrees f water temp , what would be the new temp of the water ?
    Homework Question....appreciate some help with a formula.
    Thanks
    Formula: BTU's = Lbs x Deg x SH (specific heat of material)

    Note: specific heat of water is 1.0.

    So with a little Algerbra: Btu ÷ (Lbs x SH) = Deg.

    Now to calculate Btu's required to lower temp from 72ºf to 32ºf (ICE), or 40ºf.

    62 lbs x 40 deg x 1 SH = 2480 btu's

    11532 - 2408 = 11408 btu's left at 32ºf


    Change of State - Latent heat of Fusion

    144 btu/lb to change liquid to ice : 62 lbs x 144 btu's = 8928 btus

    Now we have used : 2480 (lowering temp to 32ºf) + 8928 (change of state) = 11408 btus

    11532 - 11408 = 124 btus left


    Note: specific heat of ice is 0.5

    124 Btu's ÷ (62 Lbs x 0.5 SH) = 4 degs

    32ºf (ice) - 4ºf = 28ºf (final temperature)
    Instead of learning the tricks of the trade, learn the trade.

  10. #10
    Join Date
    Jul 2008
    Location
    Rochester NY
    Posts
    4,163
    I converted to per pound because it was easier for me to follow, would have converted back at the end had I known its only 144 to ice. Guess I assumed more because there is so much energy in condensation.

    BTW, What is that exact number?

    Did not realize its 1 btu to drop ice 2 f, so would said 30 and gotten the answer wrong even knowing cost of getting to ice. Thanks for the formula and explanation on specific heat!
    Which makes more sense to you?
    CONSERVATION - turning your thermostat back and being uncomfortable. Maybe saving 5-10%
    ENERGY EFFICIENCY - leaving your thermostat where everyone is comfortable. Saving 30-70%

    DO THE NUMBERS! Step on a HOMESCALE.
    What is comfort? Well, it AIN'T just TEMPERATURE!

    Energy Obese? An audit is the next step - go to BPI.org, or RESNET, and find an auditor near you.

  11. #11
    change of state at 212 degrees f 970 btu at this point

  12. #12
    Join Date
    Sep 2008
    Location
    VA
    Posts
    1,477
    I remember in physics we had a question:
    A round tub with 2' height, made of standard steel has a volume of 50 gallons at 50*, and it is filled with 15 gallons of 50*F water. How many gallons of boiling water would it take to over flow the tub, and at what temp would the water be? Answer to the nearest 0.001gal and 0.1*F.
    "The only true wisdom is in knowing you know nothing" Socrates

  13. #13
    Join Date
    Jul 2008
    Location
    Rochester NY
    Posts
    4,163
    I'm sure it's not as simple as 35.001 gallons and 98.6, and am dying to see the formula...
    Which makes more sense to you?
    CONSERVATION - turning your thermostat back and being uncomfortable. Maybe saving 5-10%
    ENERGY EFFICIENCY - leaving your thermostat where everyone is comfortable. Saving 30-70%

    DO THE NUMBERS! Step on a HOMESCALE.
    What is comfort? Well, it AIN'T just TEMPERATURE!

    Energy Obese? An audit is the next step - go to BPI.org, or RESNET, and find an auditor near you.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •