    I ordered a new TXV for a Traulsen model G21010, R134A 2 door reach in cooler. The original in the unit has a external equalizer connection, 1/8" swt. I believe I saw two feeder tubes on the outlet side of the TXV.
    My question, my parts supplier sent me the new TXV but it is an internally equalized valve. I just today realized so haven't called the supplier to double check the part but could it be this is an updated part and the external equalizer line unnecessary?
    The original part# 325-6080-09
    The new part sent #325-60080-27, AA 1/4 MC
    It's seems a like unit is a little too small to require external equalizer
    Apr 2001
    Quote Originally Posted by Capz View Post
    Take another look at that part #. It should be 325-60080-00.
    Also, you can see the parts list on page 17 http://download.partstown.com/is-bin...s/G210_spm.pdf
    Jabs
    Jul 2011
    Lehigh Valley, PA
    Quote Originally Posted by Jabarco View Post
    Jabs
    I see that part # in the pdf. I definitely have a part 325-60080-27, clear as day on the power head.
    I guess I am calling Traulsen on Mon to confirm no changes have been made.
    How do you guys find all of these manuals here on HVAC Talk? I spend a lot of time googling this stuff to no avail.
    Oct 2011
    Chicagoland Area
    It's all good. New valve is internally equalized. Just braze over the old external connection. I've done a bunch.
    Quote Originally Posted by 2sac View Post
    Had the same sent out. They must have done away with the internal one. Also the new ones don't have the discharge sensor on the discharge line. It is mounted on the liquid line.
    Nov 2007
    Sherman, TX
    Dang....and all these years, I thought that if the TXV fed directly into a single circuit evaporator, it didn't need an external equalizer.....and that if it had distributor tubes it needed one....
    Technical incompetence is NOT a sales tool....
    Jul 2011
    Lehigh Valley, PA
    Not sure if you miss typed, I was sent an internal equalizer TXV, the original is an external equalizer.
    How did it work out for you?
    Two feed
    With that small of evap
    You should be fine with internal.
    I've converted cap tube unit several times
    With internal txv
    No problem.
    Yep I mis typed I think I had two and they work the same. They would work better if they went with sporlan
    Quote Originally Posted by John Markl View Post
    Traulsen boxes are made in TX
    May 2003
    Utah
    If there is a refrigerant distributor you should be using an eternally equalized valve.
    Jul 2011
    Lehigh Valley, PA
    I went with Al Bundy's advice, installed the internal, brazed over the external connection. SH was at 8 to 10F. Box cooled down in a short time. The evap had two feeders.