    Barber Colman Hydraulic Valve Actuator

    I have a MP 5210-0-0-4, what is the normal position with no power, should it return to closed? Its on a Eaton Williams HX that controls temp on a Gradient coil, the temp is dropping below 74F which is the set point.

  2. #2
    Join Date
    Jul 2001
    Location
    Canada
    Posts
    1,808
    With no power to the actuator it will FAIL retracted ( valve STEM UP ) Heres the TECH sheet on it http://www.cm3web.com/parts/pdf/F24789-6.pdf

  3. #3
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,307
    Oil leaking out yet?

  4. #4
    Join Date
    Mar 2010
    Location
    Morgan Hill Ca.
    Posts
    1,219
    The spring pressure causes the actuator to retract.

    It depends on the action on the valve whether it will be open or closed.
    If a day goes by and you have learned nothing, I hope you got a lot of sleep.

  5. #5
    Join Date
    Feb 2005
    Location
    Tampa Florida
    Posts
    764
    Quote Originally Posted by Control Man View Post
    With no power to the actuator it will FAIL retracted ( valve STEM UP ) Heres the TECH sheet on it http://www.cm3web.com/parts/pdf/F24789-6.pdf
    Apparently its not returning to the retracted position, because its dropping the temp to 54F with no power to the HX. I took the actuator off the valve body and the temp went up.

    I don't normally get involved with the liquid to liquid HX's on the magnets, but I just replaced the PCO controller in the chiller, and they were getting low temp alarms on the gradient coil.


    Thanks fo the info.

  6. #6
    Join Date
    Jul 2001
    Location
    Canada
    Posts
    1,808
    GT Jets
    The spring pressure causes the actuator to retract.
    It depends on the action on the valve whether it will be open or closed.

    Hope you noticed I did not MENTION the action of the VALVE ( opened or closed ) just the position of the VALVE stem when the actuator is retracted ( No Power or control signal )

  7. #7
    Join Date
    Feb 2005
    Location
    Tampa Florida
    Posts
    764
    Control Man,

    When I screw the accuator back on with no power I could feel it forcing the valve open. Why would it force the valve open, with no power on it?

  8. #8
    Join Date
    Mar 2010
    Location
    Morgan Hill Ca.
    Posts
    1,219
    Quote Originally Posted by Control Man View Post
    GT Jets
    The spring pressure causes the actuator to retract.
    It depends on the action on the valve whether it will be open or closed.

    Hope you noticed I did not MENTION the action of the VALVE ( opened or closed ) just the position of the VALVE stem when the actuator is retracted ( No Power or control signal )

    Yep, I noticed... Was just throwing that in there for clarification that there could be three different valves (two way, three way mixing and three way bypass)...

    Also for clarification that if the spring were not in the actuator, it would not retract...

    No offense intended...
    If a day goes by and you have learned nothing, I hope you got a lot of sleep.

  9. #9
    Join Date
    Jul 2001
    Location
    Canada
    Posts
    1,808
    Could be that someone had the linkage apart to either repack the valve ot attempted to adjust it.

    If the linkage is not setup properly the valve stem will be forced down when you put the actuator on.

    Heres the info on the linkage kit http://www.cm3web.com/parts/pdf/F26279-2.pdf

    Had a school that had 150 valves repacked 1 summer by school staff , was fun the day they turned the boilers on NOT 1 would fully close as they never set the linkage properly.

  10. #10
    Join Date
    Mar 2010
    Location
    Morgan Hill Ca.
    Posts
    1,219
    Quote Originally Posted by jimp View Post
    Control Man,

    When I screw the accuator back on with no power I could feel it forcing the valve open. Why would it force the valve open, with no power on it?
    Try it again powered up but with the yellow wire isolated... The actuator has a pump inside it that runs continuously and there is a valve that opens releasing pressure and one that opens making pressure...

    You may need to hold the actuator down fairly firmly for a minute or so to push the fluid out of the piston, if it simply will not go "up" with the proper spring after a couple of minutes, the actuator is failed....

    Time to spend several hundred dollars on a new beer can...
    If a day goes by and you have learned nothing, I hope you got a lot of sleep.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event