10-06-2012, 08:34 PM #14
I'm guessing that info would be located in Mfgr. Data... Or in Maual S calculations... Is that a correct assumption? All of that should be taken into consideration when equipment selection is made? I deal with mostly Trane split h.p's, so Comfortsite will come in handy if I am correct!
-
10-06-2012, 08:36 PM #15
In this case, the system did well all summer long... So, there are no complaints on performance. I am really just screwing around with the math
-
10-06-2012, 08:48 PM #16
Also, according to manual D... This would be @ approx. .24 friction rate with 1150 fpm velocity. So, to bring the velocity into check (900), the duct should have been sized @ 9x17 @ .24 f.r.
Once again, the system operates fine... A tad fast at the registers, but no complaints (it's a rental, and it just services a floor for my 4 year old) I'm really just trying to get into the nitty gritty.
-
10-06-2012, 08:54 PM #17
That BTU rating on the equipment is for a 95°OD Db, and a 80° ID DB with a 67° WB. At lower outdoor temps you will get a greater capacity.
-
10-06-2012, 08:56 PM #18
-
10-06-2012, 08:57 PM #19
Ahhhhh... It's clicking!!! I totally lost sight of the design temp. Stuff.... Sometimes you cannot see the forest through the trees!
-
10-06-2012, 09:04 PM #20
Thanks guys! I got it.
-
10-15-2012, 06:23 PM #21
I got to borrow my boss' Alnor Capture Hood. I measured each register independently. When I added them up I only tallied 680 cfm. If you remember from my earlier post, I was calculating 820 cfm via the heat rise method. I have yet to check the Fluke 922 against that calc. I am confused as to the possibility of lost cfm. I am not able to check the return cfm as it free drafts from the pedestal to a high 20x20 rafg. Is there an explanation of this? Or do I have a user error somewhere in my experiment?
-
10-15-2012, 06:35 PM #22
Professional Member
- Join Date
- Sep 2012
- Location
- Central Florida
- Posts
- 679
-
10-15-2012, 06:59 PM #23
Don't you know, I totally overlooked that! I'm 99% sure that is the cause! Thanks man. The contractor here half a$$ed everything else, I'm sure duct sealant was not high on his list
-
10-16-2012, 04:20 AM #24