    Hello, working at a school that has automated logic BMS. I've got a whole section of the building with no communication, the computer graphics show up but I get no input reading, just a bunch of question marks. The units have power but no communication, could this be arcnet problem, or something else I'm over looking, just want to exhaust all remedies before automated logic service is brought in. Thank you

  2. #2
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    29,297
    Post Likes
    Probably better asked in the pro controls forum.

  3. #3
    Join Date
    May 2002
    Location
    Baton Rouge, Louisiana
    Posts
    4,061
    Post Likes
    Do you know which controllers are where? If you do then start at the last communicating controller and look for issues with the comm. wire, if its a daisy chain it should be either the last communicating controller or the first non communicating..................


    Unless your lucky like me, on one of the systems I installed a squirrel had his way with the comm. wire in the attic of the building, it made finding the issue real fun.
    Quote Originally Posted by MatrixTransform View Post
    very soon it is you that will be pwned

  4. #4
    Join Date
    Sep 2003
    Location
    NJ
    Posts
    127
    Post Likes
    Thread Starter
    Thank you

  5. #5
    Join Date
    Jul 2007
    Location
    Mount Airy, MD
    Posts
    7,301
    Post Likes
    Thread relocated to the Controls Section.


  6. #6
    Join Date
    May 2009
    Posts
    1,306
    Post Likes
    If you had a map of what modules are where and how the wire was run then you have a pretty good chance of finding the problem by plugging in what isn't working.
    Scott Jalbert
    WebCTRL ninja
    AX and Smartstruxure newb

    The S in IoT stands for Security

  7. #7
    Join Date
    Nov 2005
    Location
    Shreveport, Louisiana
    Posts
    2,338
    Post Likes
    You mentioned arcnet. Is there some arcnet devices on the job.
    UA Local 141

  8. #8
    Join Date
    May 2002
    Location
    Baton Rouge, Louisiana
    Posts
    4,061
    Post Likes
    Quote Originally Posted by berg2666 View Post
    You mentioned arcnet. Is there some arcnet devices on the job.
    Older Automated Logic was Bacnet over arcnet
    Quote Originally Posted by MatrixTransform View Post
    very soon it is you that will be pwned

  9. #9
    Join Date
    Apr 2009
    Location
    HR
    Posts
    49
    Post Likes
    Quote Originally Posted by joey791 View Post
    Older Automated Logic was Bacnet over arcnet
    Bacnet over Arcnet. Nice ;-) I didn't see arcnet from my highscool!

    Etheric999, I would try to check the coax cable, point to point. This can be one or two day's worth of job (two men) but you'll end with accurate map of building that's easy to debug later. You should note that ohmic correct cable is NOT always impedance correct, and that means communication would not go through. You should ude coax cable ckecker, like Fluke Intellitone or similar.

  10. #10
    Join Date
    Dec 2006
    Location
    What? Who? Where?
    Posts
    2,109
    Post Likes
    ALC is not ARCnet it is ARC156. 2 wire with a sheild not coax.

    kontrol out

  11. #11
    Join Date
    May 2002
    Location
    Baton Rouge, Louisiana
    Posts
    4,061
    Post Likes
    Quote Originally Posted by kontrolphreak View Post
    ALC is not ARCnet it is ARC156. 2 wire with a sheild not coax.

    kontrol out
    I stand corrected
    Quote Originally Posted by MatrixTransform View Post
    very soon it is you that will be pwned

  12. #12
    Join Date
    Jul 2005
    Location
    Pittsburgh, PA
    Posts
    258
    Post Likes
    You need to know your layout first. It could be something as simple as a LAN module offline and the other LAN module works, therefore you see part of the school. It could be a comm problem, if you have U or T cards it could be a sub-area network problem. Need more layout info to make a more educated guess.
    HotRod


    Controls..some days your a hero, some days your a zero. Direct acting since 1992.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.