    Sep 2003
    NJ
    Automated logic
    Hello, working at a school that has automated logic BMS. I've got a whole section of the building with no communication, the computer graphics show up but I get no input reading, just a bunch of question marks. The units have power but no communication, could this be arcnet problem, or something else I'm over looking, just want to exhaust all remedies before automated logic service is brought in. Thank you
    Southeastern Pa
    Probably better asked in the pro controls forum.
    May 2002
    Baton Rouge, Louisiana
    Do you know which controllers are where? If you do then start at the last communicating controller and look for issues with the comm. wire, if its a daisy chain it should be either the last communicating controller or the first non communicating..................
    Unless your lucky like me, on one of the systems I installed a squirrel had his way with the comm. wire in the attic of the building, it made finding the issue real fun.
    Quote Originally Posted by MatrixTransform View Post
    very soon it is you that will be pwned
    Sep 2003
    NJ
    Thank you
    Mount Airy, MD
    Thread relocated to the Controls Section.
    May 2009
    If you had a map of what modules are where and how the wire was run then you have a pretty good chance of finding the problem by plugging in what isn't working.
    Scott Jalbert
    WebCTRL ninja
    AX and Smartstruxure newb
    The S in IoT stands for Security
    Nov 2005
    Shreveport, Louisiana
    You mentioned arcnet. Is there some arcnet devices on the job.
    UA Local 141
    May 2002
    Quote Originally Posted by berg2666 View Post
    Older Automated Logic was Bacnet over arcnet
    Apr 2009
    HR
    Quote Originally Posted by joey791 View Post
    Bacnet over Arcnet. Nice ;-) I didn't see arcnet from my highscool!
    Etheric999, I would try to check the coax cable, point to point. This can be one or two day's worth of job (two men) but you'll end with accurate map of building that's easy to debug later. You should note that ohmic correct cable is NOT always impedance correct, and that means communication would not go through. You should ude coax cable ckecker, like Fluke Intellitone or similar.
    Dec 2006
    What? Who? Where?
    ALC is not ARCnet it is ARC156. 2 wire with a sheild not coax.
    kontrol out
    May 2002
    Quote Originally Posted by kontrolphreak View Post
    kontrol out
    I stand corrected
    Jul 2005
    Pittsburgh, PA
    You need to know your layout first. It could be something as simple as a LAN module offline and the other LAN module works, therefore you see part of the school. It could be a comm problem, if you have U or T cards it could be a sub-area network problem. Need more layout info to make a more educated guess.