Results 27 to 30 of 30
11-03-2012, 07:04 PM #27
Ok, standard control.
I took it that it was controlled by an od dew point controller... Which is something I'd like to find. I'm still searching for a cost effective digital version to work with your ventilating dh's.
11-03-2012, 07:58 PM #28Which makes more sense to you?
11-03-2012, 09:53 PM #29
Well, since I am an energy efficiency nut... If there is a need for dehumidification, and the OD dew point is below 50°, I want the ventilation fan and damper to operate, and leave the compressor idle. I took it from TB's earlier post that he was doing the something similar, and was curious on the control he used.
I did this to my own ventilating DH, and it works absolutely superb. The controller I'm using is an old school Carrier dew point controller that is no longer available.
11-03-2012, 10:34 PM #30
It is getting complicated. First, if the home is occupied, the home should be getting a fresh air change in 4-5 hours. This is regardless of the outdoor dew point. When the outdoor dew point is low, the moisture from the occupants is purged and the indoor %RH will be <50%. As the outdoor dew point rises, the indoor %RH will rise. Without any cooling load, the dehu will run.
If the home is unoccupied, the indoor %RH will respond to the outdoor dew point. So ventilate when occupied and dehumidify when +50%RH.
You have a good case if you have an indoor moisture source that is not occupant related. Fish tanks and open pools is a good example. I am not aware of any inexpensive dew point controllers.
We currently do not have a dew point controller but could do it based on outdoor temps and %RH.
Appreciate the comments and support.
Regards TBBear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.