Thread: American Standard Variable Speed with Emerson 1F97-1277 Help??

  1. #1
    Join Date
    Jan 2013
    Posts
    16
    Post Likes

    American Standard Variable Speed with Emerson 1F97-1277 Help??

    Hello, glad I have stumbled across this thread..a lot of good info. Hope someone can help me out on this..I have an

    American Standard Gold ZM down flow variable speed furnace 95% efficiency
    1st stage is 49,400
    2nd stage is 76,000

    The installers set me up with a Emerson (white rogers)

    Big Blue signle stage thermostat with Automatic Heat/Cool Changeover option
    Model - 1F95-1277

    Not sure on some of the settings..

    Should the T-stat be set to GAS or ELECTRIC fan setting?

    I have the T stat to slow cycle rate at 1.2 degree instead of the .6 degree for HEAT setting

    Also should I have the fast 2nd stage setting on?
    This is what fast 2nd stage setting is all about in the manual....

    Select Fast Second Stage ON or OFF – In the run
    mode, with the fast Heat feature enabled (FA Heat On), if
    the Heat setpoint temperature is manually raised by 3°F
    (2°C) or more above the actual temperature using the
    second stage will energize immediately. With FA OFF,
    second stage will not energize until the setpoint temperature
    is 1°F or more above actual temperature for more
    than ten minutes. The Fast Cool feature (FA Cool) provides
    the same controls when the setpoint temperature is
    lowered


    Thanks alot for the help..just trying to set up my home the best I can getting through Winter in Michigan. Thanks.

  2. #2
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,019
    Post Likes
    Off

  3. #3
    Join Date
    May 2009
    Location
    Cumming, GA
    Posts
    1,903
    Post Likes
    Your contractor installed your thermostat but didn't set up these options? No DIY. Call the installing contractor back out and let them properly set it up.

    Hint: You have a GAS furnace therefore the fan setting should be set on _______.

  4. #4
    Join Date
    Jan 2013
    Posts
    16
    Post Likes
    Thread Starter
    Double post.sorry

  5. #5
    Join Date
    Jan 2013
    Posts
    16
    Post Likes
    Thread Starter
    Correct. Sorry Just wanted to double check the settings, I had a leery feeling about the contractor involved..so figured I would seek out other opinions before dishing out more $ to untrustworthy 'contractors'

    It is difficult to get quality work, or maybe just my personal bad experience.

    Thank you guys for the help so far

  6. #6
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,019
    Post Likes
    Find a tech that you trust and is good at their job then sign up for a preventative maintenance contract with that company and express how you would like that tech service your unit. The contractor locator on this site should be a good place to start in finding that contractor. Most of the "best in the biz" are members of this community.

  7. #7
    Join Date
    Jan 2013
    Posts
    16
    Post Likes
    Thread Starter
    Quote Originally Posted by jtrammel View Post
    Find a tech that you trust and is good at their job then sign up for a preventative maintenance contract with that company and express how you would like that tech service your unit. The contractor locator on this site should be a good place to start in finding that contractor. Most of the "best in the biz" are members of this community.
    Will seek out that information right now. Thanks again.

  8. #8
    Join Date
    Jan 2013
    Posts
    16
    Post Likes
    Thread Starter
    Last question..seems like the furnace is running 15minutes then off for 5 minutes then back 15minutes off for 5 minutes..I have slow cycle set..going to call a tech out

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •