JCI runtime program in the NAE "LCT"
Hello,
I need to create a runtime program, in which two boilers switch every 2400 hours. My DX9100 is full, so I need to do this in the NAE using LCT. The out put of this program will switch a DCO point in the DX9100 to switch in between the boilers.
Has anyone done a runtime program in the LCT
Thanks
-
10-09-2012, 05:30 PM #2
Regular Guest
- Join Date
- Mar 2012
- Posts
- 41
The way I have done it in the past is to put runtime totalizations on the status of the pumps. Once the runtime is over 2400 hours, reset the totalization and change leads. I might be able to find a screen shot if you need one...