thanks guys.I was lost. we fixed it. we changed the time clock and the contactor it was pitted pretty bad and we also changed the defrost terminaion switch unit running good for now
JP!!!!!!
JP mod!!!!!
can we do something for breast cancer on this site????????????????????????????????????????
true knowledge exists in knowing that you know nothing.
thanks guys.I was lost. we fixed it. we changed the time clock and the contactor it was pitted pretty bad and we also changed the defrost terminaion switch unit running good for now
idk why he wanted to change the dt switch he didnt even test it but if it were bad it would not stop from defrosting would it ? it would just stop from terminating at temo right?
To the OP. Slow down. Read your wiring diagrams. They tell you everything you need to know.
Officially, Down for the count
YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET
I know enough to know, I don't know enough
Why is it that those who complain the most contribute the least?
MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING
It would not stop defrosting if the timer motor stopped while in defrost yes but most systems have a heater hi limit to stop a melt down form happening. Also if you fan delay/defrost termination failed in the termination mode, it would trigger the defrost solenoid taking it out of defrost mode as soon as it went in.
im going to guess the unit your working on is a very old semi hermetic compressor with weak valves. Let us know what you find Roy
as it turned out we changed the defrost terminators and the contactors. i think the contactors were sticking keeping the compressor running when it should have shut off
Well on some larger systems the heater won't energize till compressor shuts off. Heater relay off aux contacts on compressor contactor. Your post #13 is a good starting point to check.
Guages and electric meter will tell your problem.
[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES CMS, HVAC Electrical Specialist
Member, IAEI
AOP Forum Rules:
So,,,,you changed the DFT, the contacter, and the time clock,,,,,,Which part was faulty, or were all three bad??? I'd have a hard time billing a customer for parts that weren't needed, or maybe that's just me,,,,,,,,
One way to outthink people is to make them think you think. They'll think you're not really thinking what you're trying to get them to think you think...........
Naw, it's not just you.
[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES CMS, HVAC Electrical Specialist
Member, IAEI
AOP Forum Rules:
i have seen pump down systems that utilize a relay that is energized by out side of compressor contactor , this is done to prevent heaters from coming on during defrost , which creates high current draw and can cause breaker to trip on single units . as far as pump down goes . low psi control should be set at approx 5psi . As
others have mentioned use gauges to verify . the schematic supplied should help out ... if none available trace wires these systems are usually very simple .