Results 14 to 26 of 42
    Jan 2012
    ohio
    idk somehow reading hotter temp than actual
    NW AR
    You need to follow those steps i listed then worry about wether your heaters are coming on or not.
    Jan 2012
    ohio
    ok thanks thats what we will try
    I WILL SELL WORK,GENERATE BUSINESS, GO GET NEW CUSTOMERS!
    YOU SHUT THE HELL UP AND QUIT RUNNING YOUR MOUTH!
    Jan 2012
    ohio
    i will post back tomorrow, thanks again
    Quote Originally Posted by ar_hvac_man View Post
    Compressor shutdown doesnt initiate defrost, your clock does. Your compressor could continue to run while your heaters are energized.
    This is not necessarily true.
    Many times, the electrical circuit to the condensing unit is only large enough to run the compressor OR the heaters, but not both.
    Thus, there is often an interlock so that the compressor must cycle off before the defrost heater contactor can energize.
    NW AR
    I agree. I dont see them often but there are systems set up and wired that way. No offense to the OP but hes obviously lost(we all were at some point) so I posted what I felt he needed to tackle first.
    JP!!!!!!
    JP mod!!!!!
    can we do something for breast cancer on this site????????????????????????????????????????
    Jan 2012
    ohio
    thanks guys.I was lost. we fixed it. we changed the time clock and the contactor it was pitted pretty bad and we also changed the defrost terminaion switch unit running good for now
    Jan 2012
    ohio
    idk why he wanted to change the dt switch he didnt even test it but if it were bad it would not stop from defrosting would it ? it would just stop from terminating at temo right?
    Mar 2009
    Mid-Mo
    Quote Originally Posted by supertek65 View Post
    defrost timer de-energizes ll solenoid valve and then compressor will run until pressure switch opens.
    Hold on a second, you do refer work too??
    LMAO!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!
