Page 2 of 4 FirstFirst 1234 LastLast
Results 14 to 26 of 42
  1. #14
    Join Date
    Jan 2012
    Location
    ohio
    Posts
    144
    Post Likes
    Thread Starter
    idk somehow reading hotter temp than actual

  2. #15
    Join Date
    Mar 2007
    Location
    NW AR
    Posts
    2,478
    Post Likes
    You need to follow those steps i listed then worry about wether your heaters are coming on or not.

  3. #16
    Join Date
    Jan 2012
    Location
    ohio
    Posts
    144
    Post Likes
    Thread Starter
    ok thanks thats what we will try

  4. #17
    Join Date
    Sep 2004
    Posts
    13,930
    Post Likes
    Name:  timerio3.png
Views: 10199
Size:  74.6 KB
    true knowledge exists in knowing that you know nothing.

  5. #18
    Join Date
    Jan 2012
    Location
    ohio
    Posts
    144
    Post Likes
    Thread Starter
    i will post back tomorrow, thanks again

  6. #19
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,675
    Post Likes
    Quote Originally Posted by ar_hvac_man View Post
    Compressor shutdown doesnt initiate defrost, your clock does. Your compressor could continue to run while your heaters are energized.
    This is not necessarily true.

    Many times, the electrical circuit to the condensing unit is only large enough to run the compressor OR the heaters, but not both.

    Thus, there is often an interlock so that the compressor must cycle off before the defrost heater contactor can energize.



  7. #20
    Join Date
    Mar 2007
    Location
    NW AR
    Posts
    2,478
    Post Likes
    I agree. I dont see them often but there are systems set up and wired that way. No offense to the OP but hes obviously lost(we all were at some point) so I posted what I felt he needed to tackle first.

  8. #21
    Join Date
    Sep 2004
    Posts
    13,930
    Post Likes
    JP!!!!!!

    JP mod!!!!!

    can we do something for breast cancer on this site????????????????????????????????????????
    true knowledge exists in knowing that you know nothing.

  9. #22
    Join Date
    Jan 2012
    Location
    ohio
    Posts
    144
    Post Likes
    Thread Starter
    thanks guys.I was lost. we fixed it. we changed the time clock and the contactor it was pitted pretty bad and we also changed the defrost terminaion switch unit running good for now

  10. #23
    Join Date
    Jan 2012
    Location
    ohio
    Posts
    144
    Post Likes
    Thread Starter
    idk why he wanted to change the dt switch he didnt even test it but if it were bad it would not stop from defrosting would it ? it would just stop from terminating at temo right?

  11. #24
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    Quote Originally Posted by supertek65 View Post
    defrost timer de-energizes ll solenoid valve and then compressor will run until pressure switch opens.
    Hold on a second, you do refer work too??

  12. #25
    Join Date
    Sep 2004
    Posts
    13,930
    Post Likes
    LMAO!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!
    Quote Originally Posted by ryan1088 View Post
    Hold on a second, you do refer work too??
    true knowledge exists in knowing that you know nothing.

  13. #26
    Join Date
    Sep 2004
    Posts
    13,930
    Post Likes
    LMAO!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!
    Quote Originally Posted by ryan1088 View Post
    Hold on a second, you do refer work too??
    true knowledge exists in knowing that you know nothing.

Page 2 of 4 FirstFirst 1234 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.