walk in freezer not going into defrost
what would cause my compressor to keep runing while in defrost , this is a pumpdown system. changed time clock twice still same problem
-
10-04-2012, 07:14 PM #2
Professional Member
- Join Date
- Oct 2012
- Location
- Torrington CT
- Posts
- 69
did you have your gages on the system if it was pumping down you would see the low side drop and the high side would go i know this might be basit but if that does not happen the liquid line secanord might not be closing
-
10-04-2012, 07:17 PM #3
bad pump down solenoid or low pressure cut out. have to put your gauges on it to know which. contactor could also be welded closed.
dont just throw parts at it, troubleshoot it.
-
10-04-2012, 07:19 PM #4
Professional Member
- Join Date
- Jan 2012
- Location
- ohio
- Posts
- 120
so if my low pressure control doesnt go off on low pressure my compressor will continue to run preventing my defrost from coming on ?
-
10-04-2012, 07:20 PM #5
contactor stuck?
I WILL SELL WORK,GENERATE BUSINESS, GO GET NEW CUSTOMERS!
YOU SHUT THE HELL UP AND QUIT RUNNING YOUR MOUTH!
-
10-04-2012, 07:22 PM #6
-
10-04-2012, 07:22 PM #7
Professional Member
- Join Date
- Jan 2012
- Location
- ohio
- Posts
- 120
thanks ar. i am posting this after the fact as i tried to tell the senior tech to check solonoid and pressure cut out. i quess what i am asking is if my compressor never shuts off my time clock will never allow my defrost heaters to come on correct?
-
10-04-2012, 07:22 PM #8
defrost timer de-energizes ll solenoid valve and then compressor will run until pressure switch opens.
I WILL SELL WORK,GENERATE BUSINESS, GO GET NEW CUSTOMERS!
YOU SHUT THE HELL UP AND QUIT RUNNING YOUR MOUTH!
-
10-04-2012, 07:26 PM #9
-
10-04-2012, 07:26 PM #10
Professional Member
- Join Date
- Jan 2012
- Location
- ohio
- Posts
- 120
ok but does the defrosters come on instantly ?
-
10-04-2012, 07:27 PM #11
Professional Member
- Join Date
- Jan 2012
- Location
- ohio
- Posts
- 120
ok thats what i thought so we need to check our elements and solonoid and pressure cut out then.
-
10-04-2012, 07:29 PM #12
Professional Member
- Join Date
- Jan 2012
- Location
- ohio
- Posts
- 120
could a bad defrost termination switch also cause my heaters to not come on ?
-
10-04-2012, 07:29 PM #13
Put guages on it. Turn the clock to initiate defrost. Watch gauges. It should pump down. If it pumps down and doesnt shut off, your contactor is stuck or your low pressure cutout is bad. If it never pumps down, ll solenoid is bad. OR its wired wrong.