10-04-2012, 05:52 PM #1
Professional Member
- Join Date
- Sep 2011
- Location
- Fayetteville, NC
- Posts
- 122
True TM-24 Hot Gas condensate loop
Went to leak check this unit today. System held 225 psi for fifteen minutes. I soapy bubbled everything, nothing. Replaced the schraeders thinking that my be the problem and everything looks good. Hook up the vacuum and she pulled down and micron gauge started hanging up around 900 microns. Pump didn't sound right so I stopped and hit her again with nitrogen. By this time all the soap had ran into the condensate pan and there was a nice foamy mess down there. Removed the pan and this is what I saw.
The pan was a greasy mess as was the gas loop. I cleaned both and hit the loop with a stainless brush to get a better look at it. I thought that these stainless loops were put in to stop the leak problem.
I am guessing that awhile back someone used foam and clean on the condenser and when they rinsed it off it found its way into the pan and over an extended period of time the high temp of the loop and the sodium hydroxide did the damage. The entire loop does not look this way. Only two separate one inch sections.
Any ideas?
-
10-09-2012, 12:37 AM #2
I just had a stainless steel heated condensate pan do the same thing, only 6 months old has 2 large holes eaten into the bottom of it.
I did some research on stainless. It is just that. stain "less". It is less apt to corrode, but with acids and heat... its done for. I think you hit it with the coil cleaner not being washed out of the pan.There's no such thing as normal,Just different kinds of crazy..
-
10-09-2012, 07:53 AM #3
Regular Guest
- Join Date
- Jun 2003
- Location
- Tampa Bay, FL.
- Posts
- 118
I agree. Seen it before. Flush the system too. Probably full of moisture depending on how wet that pan gets.
-
10-09-2012, 08:13 AM #4
Hate when the coil gets so bad chemical cleaning is nessisary. These little units NOT designed with wet cleaning in mind at all. I use heavy duty paper towels and alot of them. If foaming acid cleaning is needed I have recovered and removed to clean. PIA but gotta do what you gotta do. Heavy degreaser and towels usually works pretty well.
-
10-09-2012, 08:35 AM #5
"Wet" cleaning works fine if it's done properly. It's just no one does it properly. Guess it takes too much time
In my experience, most customers don't have an issue with doing a proper job.
Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
10-09-2012, 09:24 AM #6
-
10-09-2012, 09:43 AM #7
Then they pay for it on a service call. If they only knew proper cleaning would prevent the majority of service calls
Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
10-09-2012, 10:36 AM #8
-
10-09-2012, 02:28 PM #9
Seen some other units where they wrap the tube with some kind of plastic shrink wrap. Seems like a good idea and I never had to replace one of them yet.
If You Can Dodge A Wrench You Can Dodge A Ball
-
10-09-2012, 07:45 PM #10
Professional Member
- Join Date
- Jan 2012
- Location
- ohio
- Posts
- 120
why dont they just use copper ?
-
10-09-2012, 07:53 PM #11
-
10-10-2012, 10:55 PM #12
Professional Member
- Join Date
- Sep 2004
- Location
- Phoenix, Arizona
- Posts
- 51
I've used copper for years and rarely had problems. I also only use Calgon HD cleaner. It seems to cut the animal fat just fine and does little damage to the metal parts( coils, fins...ect) I also on my condenser coils place a filter material you buy in a roll for Lennox A/C. It's thin enough to breath and grease sticks to it quickly, So I'm only washing coils 1 x a yr.. Saves on labor. I've been doing this for about 20 yrs now and it works.
-
10-11-2012, 08:06 AM #13
Regular Guest
- Join Date
- Jun 2003
- Location
- Tampa Bay, FL.
- Posts
- 118


Reply With Quote