    R410 air handler with R22 condensing unit

    I will be going back tomorrow for the 2nd time on a new install and would like some help from you pro's!
    I sold a client a 2 ton R22 air handler to go with his 2 ton straight cool XL14i condenser and we mistakenly installed a 3 ton R410 air handler (Trane) and had a call back for not enough cooling the next day. We then replaced the air handler again with the correct size but still using the R410a expansion valve. When I questioned why not replace the expansion valve I was told by management that it will work fine and no need to replace valve. And now after a few days later I find out I am going back and I have a feeling that my problem is going to be that the valve should be replaced to use R22. As I don't really know why other than its wrong. What can I tell my management to explain why it's wrong? And if it is ok to do I will just drop my argument and move on.
    Thank you in advance for your help.

  2. #2
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    It will flood the evap. The pressure in the evap is not high enough to counter the charge in the bulb. The pressure in the external equalizer is what pushes back against the bulb charge. Opposite happens when you use an R22 TXV on an R410A system, it under feeds.

  3. #3
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    It is going to be the valve. That was made clear by everyone in your last thread on the job.

  4. #4
    Join Date
    Aug 2012
    Posts
    45
    Post Likes
    Thread Starter
    Quote Originally Posted by beenthere View Post
    It will flood the evap. The pressure in the evap is not high enough to counter the charge in the bulb. The pressure in the external equalizer is what pushes back against the bulb charge. Opposite happens when you use an R22 TXV on an R410A system, it under feeds.
    Thank you for the answer, i appreciate it.

  5. #5
    Join Date
    Aug 2012
    Posts
    45
    Post Likes
    Thread Starter
    Quote Originally Posted by BaldLoonie View Post
    It is going to be the valve. That was made clear by everyone in your last thread on the job.
    I expected an answer like this as well. I realize it won't work correctly but I wanted to know why it won't work correctly. The reason for the new thread was to make it clear to me and drop all the other stuff about the job. So thank you for the useless and obvious info and for taking the time to dig and point out that there was another thread, that really helped!

  6. #6
    Join Date
    May 2009
    Location
    Cumming, GA
    Posts
    1,903
    Post Likes
    Did you install a Trane Hyperion AHU? If so, check the EEV board. There is a dip switch to swap from R410A to R22. No need to change the whole valve or stepper motor.

    Change the switch, cycle the power, and restart.

  7. #7
    Join Date
    Aug 2012
    Posts
    45
    Post Likes
    Thread Starter
    Honestly I can't tell you that yet but I am going there in a couple of hours and find out but i believe it is going to be the GAM air handler. Thanks for the input I will check it out.

  8. #8
    Join Date
    Aug 2012
    Posts
    3,771
    Post Likes
    What we have here is as failure to communicate.

  9. #9
    Join Date
    Mar 2007
    Location
    AR
    Posts
    2,489
    Post Likes
    Quote Originally Posted by toocoolforschool View Post
    What we have here is as failure to communicate.
    lol. Some men, you just cant reach

  10. #10
    Join Date
    Mar 2007
    Location
    AR
    Posts
    2,489
    Post Likes
    I bet the 3 ton ah would have worked by simply changing the txv to r22. The route taken seems backwards to me

  11. #11
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by ar_hvac_man View Post
    I bet the 3 ton ah would have worked by simply changing the txv to r22. The route taken seems backwards to me
    +1.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  12. #12
    Join Date
    Jun 2009
    Location
    Upstate SC
    Posts
    1,439
    Post Likes
    Quote Originally Posted by ar_hvac_man View Post
    I bet the 3 ton ah would have worked by simply changing the txv to r22. The route taken seems backwards to me
    +2



    Sent from my ERIS using Tapatalk 2

  13. #13
    Join Date
    Aug 2012
    Posts
    45
    Post Likes
    Thread Starter
    Seems the problem is the length of the line set. Measured the line set at 375 foot with 10-12 foot vertical rise. Found the liquid line at 67 degrees at the air handler. Spoke with Trane tech support and be said max 200 feet. He said without moving the condenser closer the only other thing I could try is lowering the fan speed which I did and it did help but not a lot. Explained that to the client and of course he gave me "we'll the original system worked fine" so now we are moving the condenser if the lowered fan speed does not work. And the Trane tech support said that having a smaller evap coil is actually helping me.

  14. #14
    Join Date
    Aug 2012
    Posts
    45
    Post Likes
    Thread Starter
    Quote Originally Posted by Brent Ridley View Post
    Did you install a Trane Hyperion AHU? If so, check the EEV board. There is a dip switch to swap from R410A to R22. No need to change the whole valve or stepper motor.

    Change the switch, cycle the power, and restart.
    Yes it is that kind of air handler and it was set for R22. Thank you

  15. #15
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    This is confusing. The first post in the thread said you have the right size, 2 tons, but still a 410 TXV. That sounds like a GAF2. But above, you saying you have a TAM4, GAM5, TAM7 or TAM8 with an EEV and it is set for 22?

    Obviously the lineset is outrageous but hard to argue with "it worked before". What kind of temp drop did you have on the liquid line when it is 67 indoors? What did it leave the condenser at? Did you check superheat? If it is a 410 TXV, beenthere says it would be flooding the coil so superheat would be zilch. If it is an EEV set for 22, you shouldn't be too far off on superheat unless low on gas or starved for gas.

  16. #16
    Join Date
    Mar 2012
    Location
    Birmingham Al
    Posts
    412
    Post Likes
    375 feet is outrageous. would have walked from that job. Have work on units with 225 that lost compressors like crazy due to oil not returning fast enough to compressor. good luck. if you have the old air handler might look at fixing what ever was wrong with it and reinstalling it.

    out of curiosity was the old unit fixed orifice? if so i would pull the piston in it and see what it was use it compared to what the unit would have come with to give you an idea of what adjustments may need to be made to the expansion valve.

  17. #17
    Join Date
    Aug 2012
    Posts
    45
    Post Likes
    Thread Starter
    Quote Originally Posted by Birmingham View Post
    375 feet is outrageous. would have walked from that job. Have work on units with 225 that lost compressors like crazy due to oil not returning fast enough to compressor. good luck. if you have the old air handler might look at fixing what ever was wrong with it and reinstalling it.

    out of curiosity was the old unit fixed orifice? if so i would pull the piston in it and see what it was use it compared to what the unit would have come with to give you an idea of what adjustments may need to be made to the expansion valve.
    Honestly I don't know what type of metering device was in the original air handler I did not look at it that much to remember. I opened up the unit to find oil all over the place and the system only at 70psi with the system not running, so I said to myself the evap coil is leaking and moved on.
    And I knew the air handler was a long ways away from the condenser but really didn't think about how long it was and that it would have an effect on the system like that. I knew it had a liquid line solenoid at the A/H and a suction line accumulator at the condenser so I guess I figured all is well. Shame on me I know.

  18. #18
    Join Date
    Aug 2012
    Posts
    45
    Post Likes
    Thread Starter
    Quote Originally Posted by BaldLoonie View Post
    This is confusing. The first post in the thread said you have the right size, 2 tons, but still a 410 TXV. That sounds like a GAF2. But above, you saying you have a TAM4, GAM5, TAM7 or TAM8 with an EEV and it is set for 22?

    Obviously the lineset is outrageous but hard to argue with "it worked before". What kind of temp drop did you have on the liquid line when it is 67 indoors? What did it leave the condenser at? Did you check superheat? If it is a 410 TXV, beenthere says it would be flooding the coil so superheat would be zilch. If it is an EEV set for 22, you shouldn't be too far off on superheat unless low on gas or starved for gas.
    That was me assuming, I apologize for that
    It was never 67 indoors that was the temp of the liquid line in the attic at the air handler.
    When I arrived it had a 6 degrees of subcooling and I don't know without looking at a pt chart or my gauges right now how much super heat I had but I can tell you that the suction pressure was 70 and the suction line temp was 87 degrees.
    I looked at the data plate of the condenser and it read 10 degrees of sub cooling so I started to add refrigerant and the head pressure did rise and the liquid line temp at the condenser fell. I stopped and started scratching my head and took a temp difference across the evap coil and it was 10 degrees. I decided to call a few other techs and was told "I dunno". I called tech support and that's when he basically laughed and was like "seriously how long is the line set?" And proceeded to explain why it won't work and to try to lower the fan speed. After I lowered the fan speed the suction line temp fell to 58 and the suction pressure of 85 and I had 14 degrees of subcooling. That's when the client arrived and I explained the problem and gave a solution. And quickly packed up and continued to run more calls as I was extremely way behind schedule and management was on my butt to get going.

  19. #19
    Join Date
    Mar 2012
    Location
    Birmingham Al
    Posts
    412
    Post Likes
    when there is really long line set it normally is stepped down like a truck line on ductwork 7/8 to 5/8 to 1/2 to the air handler. you lose capacity the entire way. the liquid line solenoid sounds like a pump down system to me is it pumping down? what brings on the compressor, a pressure switch? is the accumulator aftermarket? i have seen accumulators installed with very long line sets. also assuming it is a pump down system with that long of a line set i am thinking that the expansion valve would not settle down and run at a constant number for a while after startup like 30 min just guessing with that.

  20. #20
    Join Date
    May 2009
    Location
    Cumming, GA
    Posts
    1,903
    Post Likes
    Post some numbers. We can better understand what is happening and provide better advice with more info.

    More info = More knowledge.

    Suction Pressure? Head Pressure? SH? SC? CFM? Delta? Indoor wet bulb? Indoor dry bulb? Outdoor ambient?

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •