    Trane rover version 6

    Had a ahu controller mp580 that lost its application and program. After I downloaded the application and controller program I couldn't see the i/o's on the expansion modules. My version of rover will not do bindings but I have made changes to programs before. Do I need to have the ability to do bindings to set up the "machine bus" expansion modules? Am I missing something?

  2. #2
    Join Date
    May 2003
    Location
    Connecticut
    Posts
    476
    If it was the original configuration files they should have been in there.

  3. #3
    Join Date
    Nov 2012
    Location
    Florida
    Posts
    11
    I am assuming that you downloaded a saved program.
    Make sure that your mp580 is a version 2 or greater. I know the version 1 mp580's would not accept expansion modules.