Results 1 to 8 of 8
Thread: Tridium AX BBMD
    Nov 2005
    Sacramento, ca
    Tridium AX BBMD
    How do you add a BBMD to a Niagara panel. Do you add this under the Link tab?
    Denver, Colorado, United States
    Pardon my ignorance, what is a BBMD?
    San Diego, CA
    Quote Originally Posted by mydogsnameisbob View Post
    BACnet/IP Broadcast Management Device
    http://www.bacnet.org/Bibliography/ES-7-99/IPPART2.HTM
    Council Bluffs, Iowa
    Quote Originally Posted by stopher9 View Post
    Yes, under the link tab you can set the device as a Standard IP Device, BBMD, or Foreign Device.
    If you set it as a BBMD, the BDT table is also accessible from here to add your other BBMD's
    Quote Originally Posted by digo View Post
    Very helpful, thank you digo.
    Nov 2005
    Sacramento, ca
    Does anyone know if I need to Re-Start the station after you make the station a BBMD to be able to modify the BDT?
    Oct 2012
    Hey Chris,
    I just got off the phone with you from Controlco. I think I may have figured out where you are missing it. You mentioned that you were right clicking on the BDT and that you did not see any actions. If you just left click on the BDT it should bring up the table. Usually if everything is set up properly, the table will automatically generate but from here you can also manually add by clicking the Add button.
    Chris
    Nov 2005
    Sacramento, ca
    It will not let me add by left clicking. I am waiting for permission to cycle power because this unit is controlling a clean room. I hope it takes the configuration and up-dates the changes after the power cycle.
