  1. #41
    Join Date
    Jul 2007
    Location
    Delaware
    Posts
    3,825
    Post Likes
    Yes I like Trane. I'm just trying to figure out why you decided on Trane. You do not have Trane at this house. Did you see a commercial? Does a friend have trane? What did you do to pick trane? Was it just-on line research or do you own another house with a Trane product?
    Always here

  2. #42
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    American Standard is the "generic" version of Trane. Same equipment without the advertising markup.

  3. #43
    Join Date
    Jul 2008
    Location
    Rochester NY
    Posts
    5,298
    Post Likes
    Quote Originally Posted by catmanacman View Post
    If he diid all that and you feel comfortable with the price and the company sign the contract. Could have also made a mistake on the year of the old unit if you post the serial number someone will know what year it is . The unit he is proposing is a very nice unit
    Quote Originally Posted by catmanacman View Post
    The problem with is you can always find a hack to do do a crappy job cheaper
    Quote Originally Posted by 54regcab View Post
    Unless you live far up North I have to question the need for a 60,000BTU furnace with only a 24,000BTU cooling load.
    I do agree with others though, you found your contractor.
    Look to the lowest output. A 60 that goes to 20 could be considered SMALLER than a 45 that goes to 30. The house might only need 40 worst case, but the 60 is a better fit, it can load match across more of the season.

  4. #44
    Join Date
    Sep 2012
    Posts
    71
    Post Likes
    Thread Starter
    Quote Originally Posted by energy star View Post
    Yes I like Trane. I'm just trying to figure out why you decided on Trane. You do not have Trane at this house. Did you see a commercial? Does a friend have trane? What did you do to pick trane? Was it just-on line research or do you own another house with a Trane product?
    My first home had a Trane. My parents home has a Trane. My best friend has a Trane. But I am not married to one so I am going to check a few other options as well.

  5. #45
    Join Date
    Jun 2011
    Location
    Seattle WA
    Posts
    1,253
    Post Likes
    Trane has really done well for themselves making people think that they are better than the other major brands. I am a Trane dealer, the only reason I even offer the Trane product is for that 1 out of 20 people that believe that its going to shoot gold dust out of the registers. Otherwise I offer them Coleman/York thats significantly lower in price, has a better warranty and better heating efficiency.
    America; first we fight for our freedom,
    then we make laws to take it away.

    -Alfred E Newman

  6. #46
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,019
    Post Likes
    Libert, can you email me that manual on the York communicating zone system you were talking about in another thread, my distributer hasn't heard about it and I can't find any info. Sorry for the hijack

  7. #47
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    Quote Originally Posted by tedkidd View Post
    Look to the lowest output. A 60 that goes to 20 could be considered SMALLER than a 45 that goes to 30. The house might only need 40 worst case, but the 60 is a better fit, it can load match across more of the season.
    Please tell me where you have found a 60/20 ratio, it's what I need for my own house when it comes to replace mine. Most units I've seen do about 2/3 of full power when on low mode.

  8. #48
    Join Date
    Jul 2008
    Location
    Rochester NY
    Posts
    5,298
    Post Likes
    Infinity mvc060. Now the mod. I believe american standard, and york. I think the rheem mod goes pretty low too.

  9. #49
    Join Date
    Sep 2012
    Posts
    71
    Post Likes
    Thread Starter
    Quote Originally Posted by 54regcab View Post
    American Standard is the "generic" version of Trane. Same equipment without the advertising markup.
    Wow. Simply wow!.

    The American Standard contractor rep came out today and did pretty much the same walk-thru, testings, calculations, etc. His price was WAY over what the Trance contractor rep quoted... I mean WAY over.

    From what I can tell the quote is for the exact same equipment, but he said I needed a 2.5 ton because we like to keep the house cooler than normal. The Trane rep said 2 ton, but I didn't tell him we liked to keep it around 68-70 degrees in the summer.

    Next up. A Bryant contractor...........

  10. #50
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,329
    Post Likes
    Quote Originally Posted by Zomby View Post
    Wow. Simply wow!.

    .. The Trane rep said 2 ton, but I didn't tell him we liked to keep it around 68-70 degrees in the summer.
    ...........
    I guess some people might that it that way - if born in an igloo or similar.

    You might turn into a ZomBIE at that temperature.
    + you can $pend 2 to 3 X a$ much a$ at 77'F.
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  11. #51
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,019
    Post Likes
    With a smaller unit that removes more humidity you may be more comfortable at 72-74. Humidity has more to do with comfort than temperature.

  12. #52
    Join Date
    Sep 2012
    Posts
    71
    Post Likes
    Thread Starter
    Quote Originally Posted by jtrammel View Post
    With a smaller unit that removes more humidity you may be more comfortable at 72-74. Humidity has more to do with comfort than temperature.
    Excellent point!

  13. #53
    Join Date
    Jul 2007
    Location
    Delaware
    Posts
    3,825
    Post Likes
    You have two manual J's done. One is for a 2-Ton & the other for 2.2 Ton. The 2.2 bumped it up to 2.5. What is the temp (high) that this MJ was based on? How many days out of the year will you hit that temp? How many coolings days/hours do you have where your home is?
    Always here

  14. #54
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    Quote Originally Posted by jtrammel View Post
    With a smaller unit that removes more humidity you may be more comfortable at 72-74. Humidity has more to do with comfort than temperature.
    +1
    The 2 ton may not hold 68-70 during the hottest afternoons but the humidity will be low making it feel cooler. 68-70 at low humidity and fans running is very cool to most people.

  15. #55
    Join Date
    Jul 2008
    Location
    Rochester NY
    Posts
    5,298
    Post Likes
    Quote Originally Posted by 54regcab View Post
    +1
    The 2 ton may not hold 68-70 during the hottest afternoons but the humidity will be low making it feel cooler. 68-70 at low humidity and fans running is very cool to most people.
    Are you sure the stat is accurate? I find 78 at 40 rh is comfortable if I'm inactive, and I need 75 if rh goes above 45%. Above 50% rh, pretty hard to get comfortable without feeling clammy. You definitely want to build an understanding of how RH factors into your comfort requirements.

    I've found weight can impact tstat settings. As peoples % body fat levels increase their comfortable temperatures decreases, so things start to get delicate here, but you don't want to dismiss someone's stated setting without being cognizant of this important variable.

  16. #56
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,329
    Post Likes
    Quote Originally Posted by tedkidd View Post
    Are you sure the stat is accurate? I find 78 at 40 rh is comfortable if I'm inactive, and I need 75 if rh goes above 45%. Above 50% rh, pretty hard to get comfortable without feeling clammy. You definitely want to build an understanding of how RH factors into your comfort requirements.

    I've found weight can impact tstat settings. As peoples % body fat levels increase their comfortable temperatures decreases, so things start to get delicate here, but you don't want to dismiss someone's stated setting without being cognizant of this important variable.
    I've found that some people have Bigger Boilers [ internal, of course], so preference for 73'F or 78'F depends on boiler efficiency
    and -Bigger is not Better- can be applied in a few different ways.

    I have a big boiler but also find that 78'F at 40% R.H. is just fine!
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  17. #57
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,329
    Post Likes
    Quote Originally Posted by 54regcab View Post
    +1
    The 2 ton may not hold 68-70 during the hottest afternoons but the humidity will be low making it feel cooler. 68-70 at low humidity and fans running is very cool to most people.
    Dry Bulb 68'F
    Wet Bulb 58'F
    Dew Point 51'F
    Humidity 55%
    which is good performance from DX system in most of the U.S. at less than 3,000 foot elevation
    would probbly be considered clammy by most people.

    I would Not refer to this condition (> 42%) as Low Humidity.

    I don't know of any normally used residential equipment that actually achieves <43% at 68'F.
    Last edited by dan sw fl; 10-09-2012 at 06:07 AM.
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  18. #58
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    Quote Originally Posted by tedkidd View Post
    Are you sure the stat is accurate? I find 78 at 40 rh is comfortable if I'm inactive, and I need 75 if rh goes above 45%. Above 50% rh, pretty hard to get comfortable without feeling clammy. You definitely want to build an understanding of how RH factors into your comfort requirements.

    I've found weight can impact tstat settings. As peoples % body fat levels increase their comfortable temperatures decreases, so things start to get delicate here, but you don't want to dismiss someone's stated setting without being cognizant of this important variable.
    +1. At our house, dewpoints are under 50F all summer, so 73-75 iis very comfortable. Downstairs dewpoints are in the low 40's so 77F feels comfortable. However, when I go to my parents house wiht their oversized AC (2.5tons on a 1400sqft 2 story townshouse with 2 shared walls in Michigan (probably needs 1.5 tons based on run times alone) the humidity is over 55% and it needs ot be 69-70F ot be comfortable.

    Sorry, but 68F is either clammy if RH is over 50%, or cool if it's <50%. 68F is my winter setting in my home.

    WHat I find funny, is that some people will keep it 69F in summer and 71F in winter. Now there is a clear sign that humidity is not being managed. Heck, I had a roomate that wanted 70F in summer but I came home ot hte huse at 76F in winter.... and the dumba** is in shorts and a T-shirt.

  19. #59
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Post Likes
    Quote Originally Posted by Zomby View Post
    Wow. Simply wow!.

    The American Standard contractor rep came out today and did pretty much the same walk-thru, testings, calculations, etc. His price was WAY over what the Trance contractor rep quoted... I mean WAY over.

    From what I can tell the quote is for the exact same equipment, but he said I needed a 2.5 ton because we like to keep the house cooler than normal. The Trane rep said 2 ton, but I didn't tell him we liked to keep it around 68-70 degrees in the summer.

    Next up. A Bryant contractor...........
    Sooo a second quoat did not produce the devil? Forget the price for now. Look at the load calcs. Very close. So now you should be comfortable in knowing what you need, tonnage wise. Get the 3rd quoat then pick the one you want based on solid data. Too easy.

  20. #60
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    Quote Originally Posted by motoguy128 View Post
    +1. At our house, dewpoints are under 50F all summer, so 73-75 iis very comfortable. Downstairs dewpoints are in the low 40's so 77F feels comfortable. However, when I go to my parents house wiht their oversized AC (2.5tons on a 1400sqft 2 story townshouse with 2 shared walls in Michigan (probably needs 1.5 tons based on run times alone) the humidity is over 55% and it needs ot be 69-70F ot be comfortable.

    Sorry, but 68F is either clammy if RH is over 50%, or cool if it's <50%. 68F is my winter setting in my home.

    WHat I find funny, is that some people will keep it 69F in summer and 71F in winter. Now there is a clear sign that humidity is not being managed. Heck, I had a roomate that wanted 70F in summer but I came home ot hte huse at 76F in winter.... and the dumba** is in shorts and a T-shirt.
    We see it all the time. People want to program their thermostat that way!! Ask the customer, if it's 73 in the house, do you want to heat or AC to run? Their answer is it depends on time of year !!

Page 3 of 4 FirstFirst 1234 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •