  1. #14
    Join Date
    Jul 2008
    Location
    Rochester NY
    Posts
    4,729
    +1 to these

    Quote Originally Posted by beenthere View Post
    1400 sq ft new construction in your area shouldn't need a 2.5 ton single stage A/C let alone a 3 ton 2 stage. 2 tons should kill the place.

    A basement won't add enough heating or cooling load to need a bigger A/C or furnace.
    Quote Originally Posted by BaldLoonie View Post
    Don't bother with a "16 SEER" A/C with the GMH. You sure won't get it. I wouldn't waste the money on the GMH. If you want comfort, got to the GMVC. Otherwise stay single stage.
    45,000 Gmvc with comm stat. 2 ton 2 stage heat pump.

    Quote Originally Posted by 54regcab View Post
    A NEW 1400sqft house shouldn't need more than 50,000BTU heat just about anywhere in the continental US. If 50K wont keep a 1400sqft new house warm the insulator/air sealer failed miserably.
    Doubt a 45 will ever see high stage.
    Last edited by tedkidd; 10-06-2012 at 04:34 PM. Reason: iPad
    Which makes more sense to you?
    CONSERVATION - turning your thermostat back and being uncomfortable. Maybe saving 5-10%
    ENERGY EFFICIENCY - leaving your thermostat where everyone is comfortable. Saving 30-70%

    DO THE NUMBERS! Step on a HOMESCALE.
    What is comfort? Well, it AIN'T just TEMPERATURE!

    Energy Obese? An audit is the next step - go to BPI.org, or RESNET, and find an auditor near you.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event