    Ice-O-Matic ice machine

    Have an ice machine that mysteriously every couple weeks or so will trip the 20amp 3 pole breaker. Always happens over night when no one is around. It is probably just running trying to fill itself from being used all day. What gets me is it only happens every once in a while. Anyone ever experience this and if so what did you find to be the problem and how did you fix it? Thanks for any input!!

  2. #2
    Join Date
    Feb 2004
    Location
    Western New York
    Posts
    1,042
    Here is how I handle that problem. Go to Autozone, pick up a bunch of in-line fuse holders and slo-blow fuses. Rig the fuse into the component(s) you think might be causing the problem, with the fuse rating under the 20A breaker.

    When she quits, you should be able to ID the problem.

    Also megger the compressor first.
    Experience is what you have an hour after you need it.

  3. #3
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    120 degree water?

  4. #4
    Join Date
    Feb 2012
    Location
    Savannah, NY
    Posts
    82
    Quote Originally Posted by Tommy knocker View Post
    120 degree water?
    What do you mean by this Tommy?

  5. #5
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Quote Originally Posted by mwright View Post
    What do you mean by this Tommy?
    Haven't seen it trip a breaker but have seen it, especially on Hoshizaki machines, trip limits at night intermittently. I can see how it could cause a breaker to trip. Check the mop sink. Sometimes they have a hose with a squeeze nozzle on the mop sink. They leave both the hot and cold water on. Within a few hours of no use the hot water will heat the cold side of water system. Ice machine cycles and sump gets filled with 120 degree water and machine take a dump. They will deny this ever happens of coarse. If I suspect it is happening I will put a dab of vaseline on top of the water inlet near the solenoid. It will stay there unless the line gets hot. So when I go back and the Vaseline has melted off I have a talk with the mgr. may not be your issue but something to check. Good luck.

  6. #6
    Join Date
    Feb 2012
    Location
    Savannah, NY
    Posts
    82
    Very interesting!!! Also the Vaseline trick is ingenious!
    Thanks for the tips. I will let you know how I make out.
    If anyone else has any ideas please don't hold back.

  7. #7
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,274
    You sure breaker is not weak? Loose wire connections?

  8. #8
    Join Date
    Jun 2004
    Posts
    847
    Self contain air cool
    Make sure it does not get too hot in the room
    They shut down Ac when they leave.

  9. #9
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    17,830
    Quote Originally Posted by shaka View Post
    Self contain air cool
    Make sure it does not get too hot in the room
    They shut down Ac when they leave.
    He's not talking about a water cooled machine. He means the water input temp.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  10. #10
    Join Date
    Feb 2012
    Location
    Savannah, NY
    Posts
    82
    Quote Originally Posted by shaka View Post
    Self contain air cool
    Make sure it does not get too hot in the room
    They shut down Ac when they leave.
    The evap is water cooled.

  11. #11
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    1,375
    Quote Originally Posted by mwright View Post
    The evap is water cooled.
    technically the evaporator is water heated

  12. #12
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    17,830
    Quote Originally Posted by mwright View Post
    The evap is water cooled.
    Funny. I thought the evap was cooled by conversion of liquid refrigerant to a vapor due to a pressure drop and absorption of heat.

    I guess I better crack those books again....

    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  13. #13
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    I was talking about sump water. 120 water over evap=bad.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event